That's what I figured.
I disconnected the ends of the ring and measured ~40V to earth with a high impedence meter on both line and neutral.
Now the bit I don't get.
If you switch the RCBO off with the lever it will reset as seen at the very start of the video, but it will not reset if it's been tripped with the test button or an RCD tester.
I disconnected the ends of the ring and measured ~40V to earth with a high impedence meter on both line and neutral.
Now the bit I don't get.
If you switch the RCBO off with the lever it will reset as seen at the very start of the video, but it will not reset if it's been tripped with the test button or an RCD tester.