how do i test the r1 r2 on a lighting circuirt. and what shudd the reading be

I've never liked the idea of bunging an RCD in to work round the problem of too high a fault-loop value. On a TN system you ought to be able to get under the limit - if not then something is wrong, and saying "Oh well I'll use an RCD then" is not good.If you have a RCD on the lighting circuit then the R1 + R2 reading could be very high and the only real limit is the 3% volt drop.

There is also a TN-S system where 0.8 is subtracted instead of 0.35 but unlikely you have TN-S system.
I've never liked the idea of bunging an RCD in to work round the problem of too high a fault-loop value. On a TN system you ought to be able to get under the limit - if not then something is wrong, and saying "Oh well I'll use an RCD then" is not good.If you have a RCD on the lighting circuit then the R1 + R2 reading could be very high and the only real limit is the 3% volt drop.
However the BA22d plugs are very rare and likely you will need to just use probes on meter.........Mine is very carefully guarded both so I don't lose it and so no one uses it to power other items.

I have not said it is a work around, but that the volt drop limits are tighter so no real point in even giving figures. However if you want to suggest a ball park figure at which you would consider the ELI to be acceptable when a RCD is used I am not stopping you. No one else seems to have answered the guys question and given him any figures to go by. I realised it's easy to make a mistake when answering a question like this and I would admit any mistake if I have made any. So give some readings you would expect.I've never liked the idea of bunging an RCD in to work round the problem of too high a fault-loop value. On a TN system you ought to be able to get under the limit - if not then something is wrong, and saying "Oh well I'll use an RCD then" is not good.If you have a RCD on the lighting circuit then the R1 + R2 reading could be very high and the only real limit is the 3% volt drop.
I have to agree with BAS here![]()
Maybe you know of loads, but I can only think of one in last few years and that's a boat with on board isolation transformer, which is rather a special case.There is also a TN-S system where 0.8 is subtracted instead of 0.35 but unlikely you have TN-S system.
Why is it unlikely?

However the BA22d plugs are very rare and likely you will need to just use probes on meter.........Mine is very carefully guarded both so I don't lose it and so no one uses it to power other items.
http://www.google.co.uk/#hl=en&sour...aql=&oq=&gs_rfai=&fp=73ccac14cbe0e30c[/QUOTE]
Thanks if I ever lose mine then I know where to go.
I am sure somewhere there are houses with TN-S supplies, but I would expect to find something special like powered from their own generator.
It was because there was a slight chance, that somewhere in the country they do use TN-S supplies I made the comment.