radial circuit wiring diagram with fused spurs advice

Discussion in 'Electrics UK' started by Mahony76, 6 Mar 2017.

  1. Mahony76

    Mahony76

    Joined:
    23 Jan 2014
    Messages:
    15
    Thanks Received:
    0
    Location:
    Cornwall
    Country:
    United Kingdom
    conservatory wiring.jpg Hi, Im in the middle of building a conservatory on the side of my house and am nearing the stage where I need to install electrics. Ive drawn up a radial circuit diagram of how I think I would do it. I'll install all the wiring and sockets myself then get an electrician in to check and connect up to the house fuse box. Does this all looks ok and Is it ok to have two fused spurs off the one circuit ? cheers.
     
  2. Sponsored Links
  3. sparkwright

    sparkwright

    Joined:
    20 Aug 2009
    Messages:
    8,803
    Thanks Received:
    1,104
    Location:
    Dorset
    Country:
    United Kingdom
    Assuming all of this IS a radial circuit it's ok, BUT

    Do you really need those junction boxes?

    They aren't really a good idea if they are going to inaccessible.
     
  4. sparkwright

    sparkwright

    Joined:
    20 Aug 2009
    Messages:
    8,803
    Thanks Received:
    1,104
    Location:
    Dorset
    Country:
    United Kingdom
    The other concern is that all these sockets and any concealed wiring less than 50mm from the surface will need to be RCD protected at 30 mA, yet your diagram suggests just the outside socket is RCD protected.
     
  5. Mahony76

    Mahony76

    Joined:
    23 Jan 2014
    Messages:
    15
    Thanks Received:
    0
    Location:
    Cornwall
    Country:
    United Kingdom
    Thought it would be better than having three cables wired into the back of the socket, would it be better to just take the spurs off the sockets then like this? conservatory wiring 2.jpg cheers.
     
  6. sparkwright

    sparkwright

    Joined:
    20 Aug 2009
    Messages:
    8,803
    Thanks Received:
    1,104
    Location:
    Dorset
    Country:
    United Kingdom
    Yes, it would be better from a fault-finding point of view.

    That said, can you run the wiring in one line, without 'spurring' off?
     
  7. Mahony76

    Mahony76

    Joined:
    23 Jan 2014
    Messages:
    15
    Thanks Received:
    0
    Location:
    Cornwall
    Country:
    United Kingdom
    The armoured cable will go to the house fuse box and be wired into a 30ma RCD
     
  8. Mahony76

    Mahony76

    Joined:
    23 Jan 2014
    Messages:
    15
    Thanks Received:
    0
    Location:
    Cornwall
    Country:
    United Kingdom
    Thanks for your help :)
     
  9. Mahony76

    Mahony76

    Joined:
    23 Jan 2014
    Messages:
    15
    Thanks Received:
    0
    Location:
    Cornwall
    Country:
    United Kingdom
    Should I use a 20amp mcb in the fuse box as I'm using 2.5mm cable?
     
  10. Sponsored Links
  11. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    37,485
    Thanks Received:
    4,208
    Location:
    Retired to:
    Country:
    Portugal
    No overload protection?


    It doesn't work like that.

    upload_2017-3-6_18-57-17.png
    http://www.legislation.gov.uk/uksi/2012/3119/regulation/6/made
     
  12. endecotp

    endecotp

    Joined:
    2 Dec 2013
    Messages:
    3,949
    Thanks Received:
    507
    Country:
    United Kingdom
    In that case, there is no benefit in having an RCD outside socket. Just fit a regular weatherproof outside socket.
     
  13. oldbutnotdead

    oldbutnotdead

    Joined:
    11 Jan 2013
    Messages:
    4,543
    Thanks Received:
    946
    Location:
    Durham
    Country:
    United Kingdom
    And yes, 20A MCB for your radial as well as RCD protection. Do bear in mind what EFLI wrote- if you're lucky you'll find a local electrician who will come out, look at the job and your proposed cable runs, decide where the cables need to go, what sizes, safe zones etc etc etc. then let you throw the cabling and backboxes in, then come back and test, terminate and certify. Might be worth you getting someone to price for doing the whole job- it's not exactly massive is it?
     
  14. ban-all-sheds

    ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    69,782
    Thanks Received:
    2,858
    Location:
    London
    Country:
    United Kingdom
    When you designed the circuit, what did you work out was the Iz of the cable?
     
  15. winston1

    winston1

    Joined:
    11 Jan 2010
    Messages:
    7,202
    Thanks Received:
    556
    Location:
    London
    Country:
    United Kingdom
    In that case the outdoor socket does not to be a RCD type. No point in having two trips to reset.

    Edit. Beaton to it!
     
  16. aptsys

    aptsys

    Joined:
    16 Sep 2007
    Messages:
    1,870
    Thanks Received:
    151
    Country:
    United Kingdom
    Have you found an electrician that is happy with your proposed scheme and is happy for 3rd party test and notification of the installation?
     
  17. Mahony76

    Mahony76

    Joined:
    23 Jan 2014
    Messages:
    15
    Thanks Received:
    0
    Location:
    Cornwall
    Country:
    United Kingdom
    Yes I have, he's going to check all my wiring over and then connect to the house fuse board then provide a test certificate and register with local council
     
    • Like Like x 1