Discussion in 'Electrics UK' started by SJRSJR, 22 Jan 2017.

  1. SJRSJR

    SJRSJR

    Joined:
    25 Nov 2006
    Messages:
    484
    Thanks Received:
    6
    Location:
    London
    Country:
    United Kingdom
    Hi. Yesterday evening (TV and lamps has been on a few hours) the RCD in the consumer unit tripped taking out the MCBs on the downstairs and upstairs sockets. I re-set it which worked for 5 minutes until it tripped again. This happened several times sometimes with the downstairs MCB alone. So I left that one off and connected the TV/freeview box and two lamps to upstairs sockets via a couple of extension boards. That works fine. There is/was nothing else plugged in to the downstairs circuit (kitchen sockets are on the upstairs one) but now the RCD and downstairs MCB are tripping instantly.

    Before I call an electrician tomorrow could anyone give me an idea of what the problem might be? Thanks.
     
  2. Sponsored Links
  3. mikeyd

    mikeyd

    Joined:
    17 Jul 2007
    Messages:
    792
    Thanks Received:
    76
    Country:
    United Kingdom
    It could be a neutral to earth fault somewhere. Unfortunately as the MCB only isolates the live and leaves the neutral connected it can be a bit of a nightmare (especially without proper test equipment) to pinpoint the location, as even if the fault is on a circuit isolated by the MCB it will still trip the RCD.

    Has any work been done in the house lately, for example screwing shelves to walls, or even putting picture hooks up?
     
  4. SJRSJR

    SJRSJR

    Joined:
    25 Nov 2006
    Messages:
    484
    Thanks Received:
    6
    Location:
    London
    Country:
    United Kingdom
    Nothing done at all, does that mean (assuming no breaks in the cable) it could be a problem at the sockets? I could check them to see if anything has come loose?

    What will an electrician do?
     
  5. deadshort

    deadshort

    Joined:
    20 Sep 2014
    Messages:
    2,086
    Thanks Received:
    211
    Location:
    uk
    Country:
    United Kingdom
    Check all outdoor electrics if you have any as water ingress is often the culprit.

    DS
     
  6. SJRSJR

    SJRSJR

    Joined:
    25 Nov 2006
    Messages:
    484
    Thanks Received:
    6
    Location:
    London
    Country:
    United Kingdom
    Thanks. I have an outdoor PIR light which has been flickering recently but it's not on that circuit. Of the downstairs circuit only two sockets are used regularly. I've checked (visually that is) them both and they're fine.
     
  7. crystal ball

    crystal ball

    Joined:
    28 Apr 2004
    Messages:
    5,262
    Thanks Received:
    307
    Country:
    United Kingdom
    I would always try and eliminate the fridge/freezer, and central heating boiler / pump had a few of those causing intermittent trip problems
     
  8. SJRSJR

    SJRSJR

    Joined:
    25 Nov 2006
    Messages:
    484
    Thanks Received:
    6
    Location:
    London
    Country:
    United Kingdom
    Do you mean on any circuit or just the problem one?
     
  9. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    37,090
    Thanks Received:
    4,162
    Location:
    Retired to:
    Country:
    Portugal
    All the circuits which go off when the RCD trips.
     
  10. Sponsored Links
  11. JohnD

    JohnD

    Joined:
    15 Nov 2005
    Messages:
    73,495
    Thanks Received:
    4,232
    Location:
    Crossgates, Europe
    Country:
    Cook Islands
    The MCB is actually tripping, you say? Not just losing power because the RCD has tripped?

    Have you nailed or screwed into walls or floor recently? Do you have rodents?
     
  12. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    37,090
    Thanks Received:
    4,162
    Location:
    Retired to:
    Country:
    Portugal
    He did say:
     
  13. SJRSJR

    SJRSJR

    Joined:
    25 Nov 2006
    Messages:
    484
    Thanks Received:
    6
    Location:
    London
    Country:
    United Kingdom
    My mistake - it's just the RCD that's tripping. With the downstairs MCB off the RCD and upstairs circuit (which includes kitchen and outside light) is working okay.
     
  14. SJRSJR

    SJRSJR

    Joined:
    25 Nov 2006
    Messages:
    484
    Thanks Received:
    6
    Location:
    London
    Country:
    United Kingdom
    When I first investigated I could have sworn both (upstairs/downstairs) MCB toggles were down. Now it's just the RCD that trips when I try to put the downstairs one on.
     
  15. deadshort

    deadshort

    Joined:
    20 Sep 2014
    Messages:
    2,086
    Thanks Received:
    211
    Location:
    uk
    Country:
    United Kingdom
    You need to physically unplug every item on the circuit , if the boiler is on the circuit switch it off at the FCU.

    DS
     
  16. SJRSJR

    SJRSJR

    Joined:
    25 Nov 2006
    Messages:
    484
    Thanks Received:
    6
    Location:
    London
    Country:
    United Kingdom
    I've already done that. The only other thing that's on the circuit which I can't unplug is a light in the understairs cupboard.
     
    Last edited: 22 Jan 2017
  17. deadshort

    deadshort

    Joined:
    20 Sep 2014
    Messages:
    2,086
    Thanks Received:
    211
    Location:
    uk
    Country:
    United Kingdom
    Is it on a FCU?