I have decided to return to the first post, in case I had made an error reading it, as I am dyslexic.
”Red One” said:
I have 2 CUs in my house, box one covering lights/ cooker/ machine etc. The other box 2 is for sockets, garage and a few other things. several days ago, the RCD for box 2 tripped. After spending quite a time checking all the cabling in the box I tried to isolate which MCB the issue might be coming from, but with all MCBs off and the RCD on, any MCD I switched on tripped the RCD so I couldnt isolate the issue. I bought a new identical Wylex RCD, but same issue.
At this point it would seem a neutral to earth fault, as the fault exists with MCB’s off. With no test equipment, my next test would be to drop the neutrals for each circuit, with test equipment similar test, with isolator off test each neutral to earth.
”Red One” said:
I then went to the garage, as I suspected the issue might be in the CU thats installed there. The is covered by the RCD in the house, so only has a mains isolator at the garage CU. Again any MCD that was switched on in isolation tripped the RCD in the house.
With a suspected neutral earth fault, this was pointless, as all neutrals still connected.
”Red One” said:
SO I stripped all the wiring back from the 5 MCD's and the mains isolator, presuming that the problem electrical item was somehow "polluting" the whole CU causing an issue when any MCD was turned on. One by one, I connected back the MCDs for lights, sockets and EV charger.
Not sure if with this you are disconnecting a neutral or not?
”Red One” said:
Ultimately I isolated the problem to the cable from the EV charger . I again disconnected all the MCBs and all the negative and earth cables from the CU, and just connected the EV charger to the Mains Isolator, earth and negative. Again the RCD in the house CU tripped. The EV Charger has been running flawlessly for 3 years with no issues until now. I opened the EV charger, disconnected and reconnected the mains in wiring, the wiring to the charger cable, and all LED connectors etc. It was still tripping the RCD in the house.
OK so far.
”Red One” said:
I then bypassed the RCD in the house with the EV charger connected directly to supply. It started up as normal, was fully functional and on connection to the car, charged it as normal for 4 hours whilst I watched closely for any issues and checked the cabling periodically.
Rather naughty, but I can see the thought process, and would assume you did ensure no one could touch the car?
”Red One” said:
I know RCDs detect various faults like earth leakage etc, but the charger seems to be working quite normal without the RCD. Now, before the inevitable comments, I am not going to run the charger without the RCD in place as there is an obvious fault. I cant figure it out so will be getting a spark in. But given the information, and just for my curiosity, what could be causing this and why does the charger function normally when it receives a direct electric supply with no obvious ill effects? Many thanks.
OK,
@flameport has listed the like causes, but as to the cure, it depends on the cable used house to garage, as can’t really use the house RCD, so if the cable house to garage does not really need a RCD, and the consumer unit is the high integrity type, (three neutral bars) then move the RCD protection into the garage, using two RCD’s one for the EV and one for the rest.
If the consumer unit is not high integrity type, and the cable to the garage does not need RCD protection, then replace all but garage MCB’s with RCBO’s, and have just a MCB feed the garage. Then again, two RCD’s in the garage.
If the cable house to garage does need RCD protection, then no option, it has to be renewed.
The rest of garage only needs standard RCD protection, but the EV will need a bi-direction type, as to if type A or type B depends on the EV unit, some EV units already have a RCD, 6 mA DC detection and loss of PEN built in, but not all, so what the EV point requires, can’t really say, but it can’t share a RCD with anything else. And if charging the EV in the garage, it may not need loss of PEN detection.