Cant agree with that. A large capacity cylinder that's been run cold could take longer than that to recover and if the CH is off for 30+ mins, with people coming and going then the air temp could drop significantly.
The radiators wouldn't get too hot if the set temp was say 60 deg for the HW
But you don't need a large capacity cylinder with PDHW, that's one of the joys of it. Also, if you set 60ºC flow temperature for heating the water it'll take forever. Wants to be around 80-85 for best reheat times, which allows you to get back to heating the radiators more quickly. Trust me, I've installed a great number of systems just like this, I do know what I'm talking about ;)
It possibly can, but you don't want a Logic, too many known faults and the modulation is terrible
Modulation is 5:1, better than some others. But not wanting faults, even with long warranty. Price appeals though! Quote of £1900 for H24 changeover from 32 year old Baxi.
I think you recommended Intergas Xclusive above? I can only find combi version on the website, not system. Am I looking at the right model?
Some Intergas boilers can be changed in parameters, such as the eco rf, not sure one th xclusive.
Yeah, fair enough and not disputing that a system setup with those components and set up like that could be suitable, as you are obviously well experienced with them.
I am talking about using smart control and OT with a current system without changing out the hardware at considerable cost, to have a system that should, given the correct smart controls, be able to do what's needed. That being it can run the CH system at ~ 50deg for UFH and then raise the flow temp when the HW needs to be heated/reheated to 60deg for antibacterial purposes without any drop out of the CH.
This is all to reduce energy usage and costs, which is becoming a huge focus for my clients just now.
  • Thanks
Reactions: CBW
Can the boiler be range rated (like a combi) for CH duty because a say 10kw heating coil at 65C may now become a 15/18kw coil at 80C but if if 10kw CH range rating is required, for whatever reason, then a longer heat up time for the DHW.
Logic can do PDHW with WC or OT but it is a terrible boiler. Not only modulation is poor 6.1kw output and min pump speed is so fast that I have number of logics running on DT5 - which means that even with flow temp of 55 they hardly condense and are still much less efficient than they could be
On Logic system boiler, I'd noticed the minimum pump speed is 70%, and thought that was very fast. Others go down to 10%. Why don't they let it go lower? Very strange. As Heat only boiler, then could use own pump. 24 KW goes down to 5.1 KW which is better than many but not as good as some. But I still think I would go for a better boiler with more control. Other quotes so far are for WB 8000 and Viessman 100-W.
Wolseley also sell another Vokera system boiler called Evolve, but it's not on Vokera website.
The evolve was superceded by the Unica Max some time ago. Very similar but we changed from the aluminium exchanger in the evolve to stainless in the Unica. Very high spec of which you will possibly use 50%. I have put some videos on YouTube. Huge modulation on pump and you can set ∆T to a figure you want, there's a video on that.OT, WC etc but although it has the modbus smartkey socket any you buy at the moment will not have updated software.
I'll look it up. Wolseley website seems a bit out of date, showing Evolve and Vision non-Plus
  • Like
Reactions: CBW
This is from the Unica Max S I think but wonder how compatible this feature would be with standard or smart TRVs that keep increasing the dT as they throttle in?.,
It's all a bit confusing for me at the moment. I don't what they mean by "sanitary" or the "boiler card".
Is this a continuously variable speed pump? As the TRVs throttle in, would it need to speed up to keep the same dT?
As delivered it runs self modulating at setting 85 which can be adjusted. It will operate anywhere in the graph shaded area. If you set a parameter between 10 and 20 then the pump changes to hold that ∆T.
If TRV's close the pump will slow down rather than speed up.
'Overpumping' is the cause of narrow ∆T's.
The software adjusts the pump speed dependant on parameter settings based on current draw in auto mode.