JohnD,
Thanks for a very helpful post. I've just purchased a MEM fuse you refered to on Ebay.
Yes there is a green/yellow Earth cable that enters the flat with the supply cables (thankfully). You should be able to see it on the pic I inserted in a previous post. There is however no cable between the water supply and the MET, though the incoming water and central heating pipes have been cross-bonded. What needs to be done please? Cable size, clamps etc please.
You said
What if the fan is SELV and the transformer is outside the bathroom in the airing cupboard? Any sup bonding required, if so how?
Thanks. If you have a minute have a look at my other thread regarding installing a bathroom fan, specifically the wiring question.
Thanks for a very helpful post. I've just purchased a MEM fuse you refered to on Ebay.
Yes there is a green/yellow Earth cable that enters the flat with the supply cables (thankfully). You should be able to see it on the pic I inserted in a previous post. There is however no cable between the water supply and the MET, though the incoming water and central heating pipes have been cross-bonded. What needs to be done please? Cable size, clamps etc please.
You said
All circuits entering a bathroom should be supplementary-bonded to all metallic services entering the bathroom, so the fan supply needs to be bonded wherever you put it. But SELV downstream of the transformer must not be earthed or bonded.
What if the fan is SELV and the transformer is outside the bathroom in the airing cupboard? Any sup bonding required, if so how?
Thanks. If you have a minute have a look at my other thread regarding installing a bathroom fan, specifically the wiring question.