You tell me. What CSA cable for the radial were we talking about?Go back to the 13th edition and the rules permitted an unlimited number of number of BS1363 sockets (in domestic premises) on a 30A ring, but a maximum of only six on a 30A radial (a double socket counting as two). Where was there any logic in that?
If, per my comments, one takes the view that one cannot (should not) assume much about what might be plugged into a sockets circuit, I suppose that was not too unreasonable.The 20A radial rules then were much more restrictive, specifying a maximum of either (a) two sockets located anywhere, or (b) three sockets all in one room not exceeding 200 sq. ft. and not a kitchen (again, a double socket counting as two).
The moment one gets beyond one or two double sockets, one is into the territory of crystal balls. It is rarely the case that installing more sockets will result in the load increasing, so it's all down to judgements/guesses as regards what the load "is likely to be". FWIW, I think the OSG now recommends a minimum number of sockets for each type/size of room, and contains other odd guidances, such as limiting the number of spurred sockets on a ring final to the number of sockets on the ring, and also limiting the length of those spurs (to one eighth of total ring length, or something like that??).The 14th edition permitted a maximum of six sockets serving a single room not exceeding 300 sq. ft. and not a kitchen, otherwise limited to two as before. Then was it the 15th edition which changed it to an unlimited number of sockets within a specified area, or was that later?
Kind Regards, John