I have a strange problem on a Heatslave 18/25,
The Burner will just constantly flash Red/Orange occasionally ( once in 10 or so starts) Ive tested the motor and resistance is good (35ohm) and the grey wire throws back 50v when its running.Its just every tenth or so time it tries to fire the lockout light just flashes red/orange and nothing happens. If i leave the boiler off for half an hour it will run. Ive changed the capacitor and no change so im faily certain its the control box. As its a worcester Boiler i have the MO535 box with the reset connection (white wire) I have a spare MO535 Box without the reset link does anybody know wether i could just use the one without a reset and just leave the cbale unconnected?
Rehards
JEM3484
The Burner will just constantly flash Red/Orange occasionally ( once in 10 or so starts) Ive tested the motor and resistance is good (35ohm) and the grey wire throws back 50v when its running.Its just every tenth or so time it tries to fire the lockout light just flashes red/orange and nothing happens. If i leave the boiler off for half an hour it will run. Ive changed the capacitor and no change so im faily certain its the control box. As its a worcester Boiler i have the MO535 box with the reset connection (white wire) I have a spare MO535 Box without the reset link does anybody know wether i could just use the one without a reset and just leave the cbale unconnected?
Rehards
JEM3484