Would anyone be able to tell me what the safest approach is to terminate some unused cables that connect to an outside shed?

These connect to a non-live feed that I may wish to use in future but just now want to terminate safely.

Is a simple junction box all I need or is there a foolproof unit that I can secure all inputs to just to be sure.

The cables enters the shed from the outside (armoured) riser, I was planning to cut the cables at this point and tidy up pending further use next summer.

Thanks

Gordon
 
Nothing is foolproof.

If the cable is still connected to a supply which MAY become live a junction box, or similar would be alright.

If both ends are disconnected I would put all conductors in one terminal at both ends.
It will then be obvious that the cable is not in use.
 
If you can, good practice is to connect all disused conductors to earth.
 