The grey enclosure is part of a commercially produced item
Nice to see it's not just me who can't get DIN rail terminals to sit straight.


The grey enclosure is part of a commercially produced item
depends on the terminal make, that particular job I had far too little time to install the bars and wire them so straight terminals was way down on my list of prioritiesNice to see it's not just me who can't get DIN rail terminals to sit straight.

Oh oops - didn't think about it might be your work.depends on the terminal make, that particular job I had far too little time to install the bars and wire them so straight terminals was way down on my list of priorities![]()
The history of those internally wired stage lighting bars and dimmer: I installed them in 2007 in a school, Approx 80 hours including all of the conduit cutting/threading/bending, metal work in the restricted ceiling voidOh oops - didn't think about it might be your work.
Well it can "sometimes" be something to consider but most times its merely to consider it is worthy of considering and the answer is usually no I would not consider considering itProvided there are no'downsides', it's never really fair to criticise someone who wants to exceed 'minimum requirements', even though the CPC sizes in T+E we have are generally adiabatically adequate and large enough enough to allow the required 'maximum Zs' (for ADS) to be achieved
However, as for 'downsides', I would have to do some sums to ascertain whether this could ever be an issue, but it's just possible that increasing CPC size could sometimes be somewhat of a 'two-edged sword' - whilst that would decrease Zs (to a level lower than needed for ADS), the consequential increase in PFC might possibly render the CPC adiabatically inadequate. Watch this space whilst I 'investigate'
Kind Regards, John
MaybeWell it can "sometimes" be something to consider but most times its merely to consider it is worthy of considering and the answer is usually no I would not consider considering it
BS 7671 has a definition - namely anything/everything protected by a common OPD.What constitutes a circuit?
Yes good thinking.Maybe
When I find time to look into this ('do some sums') I might well discover that the potential issue I mentioned could never (or, at least, very rarely) arise. However, if it transpires that it IS possible for a CPC to become adiabatically inadequate ' because it is too big', that would presumably be something one should consider considering if one was contemplated a 'larger than usual' CPC?
Indeed. I often find myself having to point that out, particularly in discussions about supplementary bonding. To get 'touch voltages' (relative to 'true earth' - maybe the CPC of a different circuit), in the face of a 'zero ohms fault, down to, say, 50V, would require a CPC with a CSA almost 5 times that of the L conductor - which clearly is not realistic/'practicable'.We tend to reckon its safe to use the same as E as a Live conductor for a circuit or reduced size E that have become sort of defacto in standard T & E or 3C & E but we are probably mainly thinking of possible touch voltage of a zero ohms fault , So equal sizes become around 120V and the other sizes become higher at, notably 6.0 T & E upwards ut yet again whicher voltage results we are concentraing on mainly in the band 120 to nearing about 200v .
Thats just reminded me of a funny one John, a few years back I remember a contractor saying " Regs says Supp bonding is 4.0mm !" .Indeed. I often find myself having to point that out, particularly in discussions about supplementary bonding. To get 'touch voltages' (relative to 'true earth' - maybe the CPC of a different circuit), in the face of a 'zero ohms fault, down to, say, 50V, would require a CPC with a CSA almost 5 times that of the L conductor - which clearly is not realistic/'practicable'.
Kind Regards, John
Indeed.in the face of a 'zero ohms fault, down to, say, 50V, would require a CPC with a CSA almost 5 times that of the L conductor - which clearly is not realistic/'practicable'.
Does 543.1.1 not require any standalone 'protective conductor' (which I presume includes a SB conductor) to have a CSA of at least 4mm² unless it is 'mechanically protected'? ....Thats just reminded me of a funny one John, a few years back I remember a contractor saying " Regs says Supp bonding is 4.0mm !" .
Being pedantic I asked hime where the reg was and what does it state? nope , OK a will accept a Guidance note explanation then ? Nope.