Shower KW on a 32AMP
8 Jun 2017
Hi
Looking to a bit of help to what kw shower I need to buy for bathroom
Shower is on a Hager 32A type 2 M6 240/415V circuit breaker
Its on 10mm cable with a run of approx 4 meters
The old shower has been there 20 years and doesn't show the kw (Mira Sport 7)
I want to put a powerful shower in but not sure what is possible
Thanks in advance for any advice
About 7kW
but depending on the cable and its route you may be able to have a higher MCB. It is quite difficult for the inexperienced eye to judge.
How certain are you that it is 10mm2 cable?
What makes you think it is 10mm2 cable?
How are you 'measuring' or 'judging' this?
Have to ask this, or else we may go down the wrong road.
Was hoping for more than 7kw :(
Cable measures 17mm wide and from what I've read that should be 10mm??
I'm getting an electrician to wire up when I have finished the suite/tiling but looking at shower options first
Maybe get the electrician in before tiling etc to change the cable for a bigger one if needs be!
Look at the earth conductor in the cable. If it is stranded, it is 10 milli.
Thanks, had a look today and it is stranded so must be 10mm
Does that mean I can get more than a 7k shower on the 32 amp. The one I want has a minimum kw of 8.5
Calculate 32amp multiplied by 230volt to find the maximum watts your MCB can supply.
Your existing set up can only deliver 32x230 = about 7.3KW.
The limit on the current is set by the 32A MCB.
If your cable is 10mm², this can support more than 32A. This is can be achieved by first checking the EFLI of the circuit, and then a larger MCB could be fitted that will allow more current. This nedds to be done by an electrician who will also need to check that the supply is suitable for the higher current and also other factors - some older fuseboxes are not built for circuits that are higher than 30ish amps.