    I have a customer who has bought 2 single ovens both drawing approx 3.4kw. Instructions state not to be connected to plug top/sw spur, fair enough.
    Existing cooker wired in 6mm back to board on 32a mcb. When met with this situation before have wired new circuit back to board with 16 or 20a mcb and downrated existing mcb to same to cover both ovens.
    Its a no no to run new cable back to board, tiles, laminate, panelling etc.
    Only option I can think of is 2 module enclosure with 2 16a mcb`s. This can be mounted in housing top box. Any thoughts? Would you still have 2 20a D.P switches for isolation or are the 2 mcb`s sufficient for this purpose.?
     
  2. Sponsored Links
  3. riveralt

    riveralt

    Joined:
    4 Jan 2004
    Messages:
    4,020
    Thanks Received:
    597
    Country:
    United Kingdom
    Are you saying you are a qualified electrician because if you are you should certainly know the answer the question you are raising.
    Do you understand the purpose of an MCB?
    Do you know how to calculate diversity?
    At the very least you be able to find a solution in the on site guide.
     
  4. ban-all-sheds

    ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    69,782
    Thanks Received:
    2,858
    Location:
    London
    Country:
    United Kingdom
    Looking at his previous posts it seems that he definitely claims to be.
     
  5. ebee

    ebee

    Joined:
    14 Aug 2005
    Messages:
    1,713
    Thanks Received:
    29
    Location:
    Lancashire
    Country:
    United Kingdom
    Three reasons that you might be using a certain MCB & cable combination in any circuit.

    1/ Short circuit

    2/ Earth fault

    3/ Overload

    If the load is limited by virtue of its characteristics ie it is a fixed load like a cooker or shower then you might not need 3/.

    If you decide that an earth fault is covered by an RCD then you might not need 2/

    (although most designers would only consider this in a TT installation and still rely on 2/ and merely consider the RCD to be a back up protection in this respect in a TN installtion)

    It might be best to consult an electrician if you going down the building control notification route
     
  6. PrenticeBoyofDerry

    PrenticeBoyofDerry

    Joined:
    30 Jun 2009
    Messages:
    21,627
    Thanks Received:
    2,382
    Location:
    Londonderry
    Country:
    United Kingdom
    So what about when you are considering the rating of DP switches? As the OP surprisingly :eek: has a problem with this!
     
  7. plugwash

    plugwash

    Joined:
    28 Mar 2004
    Messages:
    9,534
    Thanks Received:
    375
    Country:
    United Kingdom
    Getting back on topic what do the manufacturers instructions say? Do they specify a specifc rating (or range of ratings) of protective device must be used? if so what do they say? If they say "max MCB 20A" or whatever then you need to respect that.

    If you are planning to hide the box containing the MCB then you should provide easilly accessible switching like you would with any cooker to allow it to be turned off quickly in the event of problems.
     
  8. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
  9. Sponsored Links
Loading...

Share This Page