Single wall socket connected to two Mini Circuit Breakers.

Discussion in 'Electrics UK' started by Daniel Keenan, 18 Aug 2020.

  1. Taylortwocities

    Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    19,621
    Thanks Received:
    1,993
    Location:
    Oxfordshire
    Country:
    United Kingdom
    At the time of installation it would have proved that wires 1&2 were the ends of ring 1. And that wires 3&4 were the ends of ring 2. He may have done this test but he mixed them up when he fitted the ends to the MCBs.
    It doesn’t reveal an interconnected ring later on.
     
  2. Sponsored Links
  3. Taylortwocities

    Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    19,621
    Thanks Received:
    1,993
    Location:
    Oxfordshire
    Country:
    United Kingdom
    Yes, it is. It’s a spur, same as any other. Except the connection has been made at the MCB not at a socket. Perfectly normal.

    But, like any spur, you can only have one socket, not two or three on the one spur.
     
    • Thanks Thanks x 1
  4. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    33,985
    Thanks Received:
    3,723
    Location:
    Retired to:
    Country:
    Portugal
    Yes, it is protected by the fuses in the plugs - 2 x 13A = 26A - which is why only one double socket is allowed on the unfused spur.

    Just to confuse matters, although two single sockets would be the same, some say certain words in the regulations prohibit two singles.
    Electrically it would be fine.

    You can always use 4mm² cable for the unfused spur then have more sockets.
     
    • Thanks Thanks x 1
  5. gman76

    gman76

    Joined:
    19 Jan 2006
    Messages:
    544
    Thanks Received:
    30
    Location:
    Wiltshire
    Country:
    United Kingdom
    Of course - thanks TTC. Bit of a brain fart this evening! Not being an electrician, I don't live & breath this stuff every day!
    Thanks for clearing that up.
    Luckily, I don't think the OP wants to spur from the added socket, so FCU issue averted.
    Thanks too to EFLI.
     
  6. Daniel Keenan

    Daniel Keenan

    Joined:
    18 Aug 2020
    Messages:
    10
    Thanks Received:
    0
    Country:
    United Kingdom
    Thanks TCC, I understand all of this. I just want to add another socket directly to the ring from a socket that is not from a spur but was originally built with the house. That's perfectly fine isn't it?.
     
  7. Daniel Keenan

    Daniel Keenan

    Joined:
    18 Aug 2020
    Messages:
    10
    Thanks Received:
    0
    Country:
    United Kingdom
    Can you add 4mm² cable to an already existing 2.5mm² final ring circuit? Does this not overload the 2.5mm² or does the circuit compensate by distributing the load evenly on both sides of the spur (which are using the 2.5mm²)?
     
  8. Taylortwocities

    Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    19,621
    Thanks Received:
    1,993
    Location:
    Oxfordshire
    Country:
    United Kingdom
    Yes, if it is on the ring itself and not already a spur.
     
  9. Taylortwocities

    Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    19,621
    Thanks Received:
    1,993
    Location:
    Oxfordshire
    Country:
    United Kingdom
    Really? I don’t think so.
     
  10. Sponsored Links
  11. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    33,985
    Thanks Received:
    3,723
    Location:
    Retired to:
    Country:
    Portugal
    Yes.

    No. Not per se.

    Only evenly if in the centre of the ring - but
    27A is so near 32A that enough to overload it would have to be very near one end.

    Plus, of course, there could be two or more 2.5mm² spurs close together so the fact that one might be 4mm² does not raise any separate concerns.
     
  12. Taylortwocities

    Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    19,621
    Thanks Received:
    1,993
    Location:
    Oxfordshire
    Country:
    United Kingdom
    Have I misunderstood this
    To me, this says that (in your opinion) you can connect a bit of 4mm² cable as a spur to a 32A protected 2.5mm² ring final. then string 5 double 13A sockets on the end of the 4mm² Cable??

    Is that what you mean?
     
  13. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    33,985
    Thanks Received:
    3,723
    Location:
    Retired to:
    Country:
    Portugal
    Yes, with the already mentioned proviso that it is not too near one end that it would cause a problem - as would 5 separate spurs.
     
    • Like Like x 1
  14. Taylortwocities

    Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    19,621
    Thanks Received:
    1,993
    Location:
    Oxfordshire
    Country:
    United Kingdom
    Not according to app 15. If what you have stated is allowed then we can all connect 4mm SWA to ring finals, run it down our gardens and put consumer units on the end.
     
  15. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    33,985
    Thanks Received:
    3,723
    Location:
    Retired to:
    Country:
    Portugal
    Appendix 15 is only informative and not exhaustive.

    If 32A is enough for the garden circuit, then why not? Why would you mention a consumer unit?
     
    • Like Like x 1
  16. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    33,985
    Thanks Received:
    3,723
    Location:
    Retired to:
    Country:
    Portugal
    Tell us why Appendix 15 apparently 'prohibits' two single sockets on a 2.5mm² unfused spur.
     
  17. sparkwright

    sparkwright

    Joined:
    20 Aug 2009
    Messages:
    7,598
    Thanks Received:
    935
    Location:
    Dorset
    Country:
    United Kingdom

    This is fine, if the 4mm2 is connected to a socket or joint DIRECTLY on the ring (ie not a spur), and the cable to the new 5 sockets would have to be in 4mm2 (though the very last one could be 2.5mm2.

    I also don't see a problem spurring in 4mm2, then forming an additional little ring from there onwards in 2.5mm2.


    Not that I would do much of this in reality - makes the testing a pain for a start.
     