sixe of earth link?

pdcelec said:
ban-all-sheds said:
Supplementary bonding is what is applied to extraneous-conductive-parts in some locations.

Back boxes are not extraneous-conductive-parts, therefore any bonding conductors are not supplementary ones.

Supplementary bonding can also be applied to exposed conductive parts

ie Socket mounting screws etc
 
Sponsored Links
looks like there's differences of opinion!
i've got a reel of 1.5mm earth from a while back, so i'll use that.
thanks for the replies.
 
If the size of your cpc is 1.5mm2 and you are connecting an exposed conductive part to an exposed conductive part (which you are) and the cable is mechanically protected (which it will be), then 1.5mm2 is correct
 