Slow pressure drop on worcester bosch boiler

Joined
13 Feb 2025
Messages
359
Reaction score
7
Country
United Kingdom
Have a Worcester Bosch oil combi boiler with a slow pressure drop (drops from 1.5 bar to 1 bar over 2 months). Boiler feeds about 12 rads. Property is a bungalow. Have checked multiple times for leaks can't see any either by rads or under floor. Pipework is clipped to joist no screed or concrete/cement embedded pipes (all pipework). Zero sign of pipe leaks . I top up with inhibitor and leak sealer regularly. Only thing I can think of is insufficient inhibitor (fernox).
 
At that slow a rate of loss it's almost always a weep that's evaporating before it ever shows, so I'm not surprised you've found nothing visible. The quickest way to narrow it down is to isolate the boiler from the system overnight - if the boiler side holds pressure and the system side drops, the leak is in the pipework and you can work round the rad valves and joints one zone at a time. Also worth checking the expansion vessel charge, as a flat one will push a little water out of the PRV every cycle and it looks exactly like a mystery leak.
 
The PRV inside the boiler?
Ok long discussion just found this out. The property has 14 rads according to https://boilersizecalculator.com/ (14 rads property and large type 22 rads (oversized) and 22mm flow/return pipework) the expansion vessel should be 18 litre (see attachment) but the expansion vessel is only 12 litre. Boiler was installed in 2020, the expansion vessel was recharged in 2024, and basically since 2020 but especially from 2025 the pressure has been dropping from 1.5 bar (default top up level) to 1 bar. Boiler is Greenstar Heatslave II 18/25.

To recharge an expansion vessel properly the whole heat loop needs drain down and that has never been done on any boiler service and expansion vessel recharge/inspection (e.g. air leak through schrader valve) inspection is annual but only done once without drain down in 6 years. Only 1 job card says the expansion vessel (EV) recharge/inspection in 2024 the others do not specify EV recharge.

Twice now in 2 months the boiler has made gurgling/sucking noises when the pressure has dropped to about 0.9 bar (just below 1-2.75 bar optimal range) after topping up to 1.5 bar the day prior.

EV's only last 5-10 years so it's due for replacement.

Here's the 12 litre EV in use: https://www.screwfix.com/p/worcester-bosch-87161076600-12ltr-expansion-vessel/704TR?utm_source=bing&utm_medium=cpc&utm_campaign=Bing_UK_Shopping_PMax_Heating & Plumbing&utm_term=2331720565763881&utm_content=Heating & Plumbing&gclid=1efb59a3c4b51ab98490336867ddb2f7&gclsrc=3p.ds&gad_source=7&gad_campaignid=22478593832#product_additional_details_container

A youtuber (here:
) says EVs are commonly undersized and shortens the boiler lifespan. Typically since 2023 first thing in morning the boiler pressure is 1 bar but goes up to 1.5bar when hot (on).

Attached is a pic of the EV - should I press the schrader valve seat and see if water comes out? Water either leaks out the air release valve (schrader) or the EV's PRV (at the back? Can't see it on the front)

I think I need to get an additional 6/12 litre expansion tank and put on flow/return (which one?) loop to add expansion capacity regardless of this leak as this should prolong life of the boiler particularly as I'm enlarging the rads (e.g. changing from type 22 600mm high x 1m wide to 600mm high x 1.5m wide) in cold bedrooms.
 

Attachments

  • 2026-10-10 ty cwm oil boiler 14 rads expansion vessel requirement.png
    2026-10-10 ty cwm oil boiler 14 rads expansion vessel requirement.png
    662.4 KB · Views: 15
  • expansion vessel.PNG
    expansion vessel.PNG
    1.1 MB · Views: 18
Last edited:
At that slow a rate of loss it's almost always a weep that's evaporating before it ever shows, so I'm not surprised you've found nothing visible. The quickest way to narrow it down is to isolate the boiler from the system overnight - if the boiler side holds pressure and the system side drops, the leak is in the pipework and you can work round the rad valves and joints one zone at a time. Also worth checking the expansion vessel charge, as a flat one will push a little water out of the PRV every cycle and it looks exactly like a mystery leak.
I have 2 magnaclean (magnetic) filters 1 on flow 1 on return. If I turn off the boiler then isolate both filters then charge boiler to 1.5 bar then check next morning. If still at 1.5 bar then leak is on rad side if not then leak is on boiler side? I've checked all rad lockshield (under cap) and the automatic air vent (installed on air rads, manufacturer is Aladdin. They fail shut after 5 years) and can't find any leaks at all. Most of pipework is hep2o installed by myself checked for leaks repeatedly used huge amounts of pipeclips.
 
Check the pipe that goes to the outside.
Checked the high pressure discharge line from EV it doesn't look used and is covered in cobwebs. Should I screw a cup directly beneath this outlet to see if it captures discharged water? This discharged water would indicate EV issues
 
If I turn off the boiler then isolate both filters then charge boiler to 1.5 bar then check next morning. If still at 1.5 bar then leak is on rad side if not then leak is on boiler side?
Yes, try that.
Should I screw a cup directly beneath this outlet to see if it captures discharged water? This discharged water would indicate EV issues
Yes, or tie a plastic bag over it.
 
Have a Worcester Bosch oil combi boiler with a slow pressure drop (drops from 1.5 bar to 1 bar over 2 months). Boiler feeds about 12 rads. Property is a bungalow. Have checked multiple times for leaks can't see any either by rads or under floor. Pipework is clipped to joist no screed or concrete/cement embedded pipes (all pipework). Zero sign of pipe leaks . I top up with inhibitor and leak sealer regularly. Only thing I can think of is insufficient inhibitor (fernox).
Irrespective of the system volume contents, rads etc, a 12L EV with charging/filling pressures of 1.0/1.5bar will lose 2.4L every time the pressure falls from its filling pressure of 1.5bar to its charging pressure of 1.0bar, 2.4L in 2 months is 14.4L per annum, very excessive IMO, you might expect, at most, maybe total top up to be ~ 2/2.5L/annum.

The 12L EV will accomodate 140L of system water 2.73L expansion at 65C in rising to 2.50bar (no problem with lifting the PRV) and will accomodate 3.28L of expansion from 168L of system water in rising to 2.73bat, still comfortably short of the 3.0bar PRV lifting pressure, a 14rad system should be OK but no harm in installing a bigger EV, you can't oversize it.
 
Irrespective of the system volume contents, rads etc, a 12L EV with charging/filling pressures of 1.0/1.5bar will lose 2.4L every time the pressure falls from its filling pressure of 1.5bar to its charging pressure of 1.0bar, 2.4L in 2 months is 14.4L per annum, very excessive IMO, you might expect, at most, maybe total top up to be ~ 2/2.5L/annum.

The 12L EV will accomodate 140L of system water 2.73L expansion at 65C in rising to 2.50bar (no problem with lifting the PRV) and will accomodate 3.28L of expansion from 168L of system water in rising to 2.73bat, still comfortably short of the 3.0bar PRV lifting pressure, a 14rad system should be OK but no harm in installing a bigger EV, you can't oversize it.
Boiler feeds 14 rads my mistake. OK so if I get either 1) Bigger EV to replace the 12 litre existing EV, 2) Get another 6 or 12 EV install alongside the existing EV either in the boiler or on flow/return. I can't find a bigger EV than 12 litre one. Is the easiest think to do is to get another 12 litre EV and install alongside (this way https://www.ultimatehandyman.co.uk/how-to/expansion-vessels/?)
 
Last edited:
Irrespective of the system volume contents, rads etc, a 12L EV with charging/filling pressures of 1.0/1.5bar will lose 2.4L every time the pressure falls from its filling pressure of 1.5bar to its charging pressure of 1.0bar, 2.4L in 2 months is 14.4L per annum, very excessive IMO, you might expect, at most, maybe total top up to be ~ 2/2.5L/annum.

The 12L EV will accomodate 140L of system water 2.73L expansion at 65C in rising to 2.50bar (no problem with lifting the PRV) and will accomodate 3.28L of expansion from 168L of system water in rising to 2.73bat, still comfortably short of the 3.0bar PRV lifting pressure, a 14rad system should be OK but no harm in installing a bigger EV, you can't oversize it.
Is the PRV (that pipes excess water out) at the back of the boiler?
 
Irrespective of the system volume contents, rads etc, a 12L EV with charging/filling pressures of 1.0/1.5bar will lose 2.4L every time the pressure falls from its filling pressure of 1.5bar to its charging pressure of 1.0bar, 2.4L in 2 months is 14.4L per annum, very excessive IMO, you might expect, at most, maybe total top up to be ~ 2/2.5L/annum.

The 12L EV will accomodate 140L of system water 2.73L expansion at 65C in rising to 2.50bar (no problem with lifting the PRV) and will accomodate 3.28L of expansion from 168L of system water in rising to 2.73bat, still comfortably short of the 3.0bar PRV lifting pressure, a 14rad system should be OK but no harm in installing a bigger EV, you can't oversize it.
Also according to boiler sizing a 14 rad property should have a 30 kW boiler not a 18/25 kW boiler so the boiler itself is undersized. And the rads themselves are oversized
 
A oil fired boiler contains ~ 20L more water than a gas fired one so another 12L EV installed with the other one should give ample room for expansion with a very low final pressure, if you're getting someone to install it then you might be better off just getting two new ones as the existing one might be near its end of life and if renewed now will extend the renewal time.
If the rads are zoned then a 18/25kW boiler should be adequate IMO.
 