Socket Tester error only when shower is running

Discussion in 'Electrics UK' started by TM1303, 6 Oct 2019.

  1. TM1303

    TM1303

    Joined:
    20 Mar 2018
    Messages:
    11
    Thanks Received:
    2
    Location:
    Chepstow
    Country:
    United Kingdom
    Evening.

    After testing every plug socket in the house and finding them all to be ok, I left the socket tester plugged in to a socket with the switch switched off. I didn't leave it plugged in intentionally, I'm just lazy.

    Days later, I'm in the kitchen and all of a sudden the socket tester starts buzzing even though the socket is switched off. Curious. The error code (one red, pictured below) isn't listed on the tester, the plot thickens. Switching on the socket and the OK code shows, switching off and we're back to this unlisted error code.

    And without warning, the error clears.

    It didn't take too long to work out that when the electric shower is running the switched off socket shows this error. When the shower stops it clears. I moved the socket tester and find the same behaviour throughout the house.

    It's an old house with trad wire colours, but we have a modern RCA board with the shower and the mains on different switches.

    Any idea what this all means?

     
  2. Sponsored Links
  3. 333rocky333

    333rocky333

    Joined:
    12 Jan 2008
    Messages:
    7,319
    Thanks Received:
    699
    Location:
    Essex
    Country:
    United Kingdom
    Do you know what make sockets you have, if not post a picture.
    It may be they are single pole switched and there picking up a stray voltage between E and N, possibly induced by the high current used by the shower. if you have a multimeter you may be able to safely measure this voltage
     
    • Like Like x 1
  4. RF Lighting

    RF Lighting

    Joined:
    31 Mar 2006
    Messages:
    19,107
    Thanks Received:
    1,222
    Location:
    Leeds
    Country:
    United Kingdom
    Sounds like a high resistance earth and possibly a fault of some degree on the shower heater element to earth
     
  5. Harry Bloomfield

    Harry Bloomfield

    Joined:
    30 Dec 2018
    Messages:
    1,971
    Thanks Received:
    240
    Country:
    United Kingdom
    I would suggest it is just an increase in PD (voltage) between N & E, due to the resistance of the neutral when it came under higher load of the shower. Nothing to worry about.
     
    • Thanks Thanks x 1
  6. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    29,836
    Thanks Received:
    3,214
    Location:
    Retired to:
    Country:
    Portugal
    As these testers cannot distinguish between Neutral and Earth, can that be deduced?
     
  7. Harry Bloomfield

    Harry Bloomfield

    Joined:
    30 Dec 2018
    Messages:
    1,971
    Thanks Received:
    240
    Country:
    United Kingdom
    I believe so, lacking a live, the electronics would be back fed by the PD between L & N.
     
  8. FrodoOne

    FrodoOne

    Joined:
    20 Feb 2017
    Messages:
    312
    Thanks Received:
    32
    Location:
    Melbourne, Australia
    Country:
    Australia
    This could be a problem with a high resistance neutral (connection) to the supply.

    I strongly suggest that you measure the voltage on the Neutral with respect to Earth when the shower is not in use and when it is.
    If the voltage rises "significantly" you could have a faulty Neutral connection.

    https://www.commerce.wa.gov.au/site..._report_-_final_version_25_september_2019.pdf details the result of a faulty neutral connection eventually going open circuit.
     
  9. aptsys

    aptsys

    Joined:
    16 Sep 2007
    Messages:
    1,657
    Thanks Received:
    123
    Location:
    Cambridgeshire
    Country:
    United Kingdom
    Do you have an earth rod/TT supply?
     
  10. Sponsored Links
  11. andy11

    andy11

    Joined:
    19 Apr 2005
    Messages:
    536
    Thanks Received:
    48
    Country:
    United Kingdom

    Very interesting reading. Did the girl survive? The report doesn't say whether she did or not; although the report doesn't refer to the electric shock as a "fatal electric shock".

    The moral of the story is: tighten the screws fully and don't nick the conductors.
     
  12. JohnD

    JohnD

    Joined:
    15 Nov 2005
    Messages:
    59,997
    Thanks Received:
    3,092
    Location:
    21st Century
    Country:
    Cook Islands
    I had a lost neutral in 3ph commercial premises once (damage in the road) and the voltage zoomed up and down damaging quite a lot of stuff.
     
  13. FrodoOne

    FrodoOne

    Joined:
    20 Feb 2017
    Messages:
    312
    Thanks Received:
    32
    Location:
    Melbourne, Australia
    Country:
    Australia
    Further information at https://www.abc.net.au/news/2019-09...en-tap-electrocution-report-released/11553734

    This "situation" was discussed on https://www.renovateforum.com/f195/dangers-neutrals-126786/, which you may care to read.

    I do hope that TM1303 is taking this information into consideration!
     
    Last edited: 9 Oct 2019
  14. FrodoOne

    FrodoOne

    Joined:
    20 Feb 2017
    Messages:
    312
    Thanks Received:
    32
    Location:
    Melbourne, Australia
    Country:
    Australia
    Given the advice and examples quoted, it is quite concerning that TM1303 has not responded in the 4/5 days since the original post.
    One must hope that he/she has acted to locate and correct what may be a quite serious problem - and I am not joking when I write this.

    A response from TM1303 would be appreciated
     
  15. Colin Brenton

    Colin Brenton

    Joined:
    1 Mar 2008
    Messages:
    91
    Thanks Received:
    13
    Country:
    United Kingdom
    Switch the socket on...
     
  16. Colin Brenton

    Colin Brenton

    Joined:
    1 Mar 2008
    Messages:
    91
    Thanks Received:
    13
    Country:
    United Kingdom
    Sorry, please ignore my post - that'll learn me to not read the thread properly before posting!
     
  17. TM1303

    TM1303

    Joined:
    20 Mar 2018
    Messages:
    11
    Thanks Received:
    2
    Location:
    Chepstow
    Country:
    United Kingdom
    Sorry for not getting back to you, this is basically what the electrician said ^ and he's a good egg.

    Thanks all for your concern and your input, always valued x
     