Basic idea is cable is protected from overload either by what it feeds or by what it is fed from, since all plugs in UK are fused it is permitted to rely on that fuse, but that only works if feeding one device, i.e. single socket, double socket, or fused connection unit (FCU) and for any new also must be RCD protected.
Protection is also done on the supply side, but a 2.5 mm² cable is only considered as good for 20 amp, (it does change according to how fitted so that is the minimum valve permitted for a cable used for a ring final) so it needs feeding from both sides so in effect the cable is doubled up, and feed from a 30 amp fuse or 32 amp MCB/RCBO, this is the whole idea of the ring final. However we can also use heaver cable 4 mm² for example and feed as a radial, and still use the same protective devices, so just because it is fed with a 32 amp trip does not mean it is a ring final.
We can also of course use a 20 amp overload and 2.5 mm² cable as a radial, however with a ring to keep within the volt drop requirements we can use 106 meters of cable, but with radial at 20 amp only 32 meters, so for years the ring final has been the preferred method.
Because the ring final is considered the final circuit hence the name, we don't call a fused radial from it a radial which really it is, but a fused spur, not sure why but it is, and when relying on the fuse in the plug we call it a spur or unfused spur.
So job one should be work out what the socket is that we are taking the new socket from, if previous people have followed the rules, then if it has two cables, or supplied with a 25 amp or less overload, then if also RCD protected you can take a spur, however that is assuming no one has broken the rules before you, my dads house had unfused spurs off unfused spurs every where, and also fused spurs off fused spurs, clearly my dad did not know the rules, he told me he was very proud when he moved into the house in 1954 as it had 6 sockets, and my granddads house only had two. When finally re-wired found wooden back boxes as well, official as makers name on them. OK a lot was wired in the old 7/0.036 cable which is a little thicker than 2.5 mm² but some cable did show signs of over temperature damage.
In theory we should test the loop impedance as well as supply protective device size, and also tripping times for the RCD, so in theory sockets should not be added by DIY guys as they don't have the test equipment, in practice we know it is regularly done, and also errors made, in theory every 10 years (5 years with rental property) or change of occupant all wiring should be tested, but with owner occupied houses that rarely happens.
So take some time and read up on how ring mains work, then see what you have, and decide if you can extend, there is no point any one on here saying no you must not fit your own sockets, this is UK not Australia, we have not passed laws to stop DIY yet. But clearly care is required.