Goldberg
I'm not trying to spin anything - Chri5's comment was incorrect in the context of this topic.in the absense of you explaining WHY he's wrong, then your coment of "you're wrong" to a stateent that is categorically true, then it it you that is wrong.. no matter how you try and spin it.
If you reword his comment into something else, and put it in a different context, then I agree that it would be correct.
For example: An unfused spur from a ring final circuit can't carry the load of two sockets if it is run in 2.5mm² T&E.
But do you still think this holds true in all circumstances?
Really? How about if the T&E was in conduit in thermal insulation? I can't see how it would carry 26A safely.the comment that "A single spur from a ring circuit in 2.5mm TE can handle 1 x double socket." is absolutely correct.
And before you start down the track of saying that a double socket can't support 26A, there's nothing to stop someone plugging two 3kW loads into a double socket.