Customer call today. Intermittent loss of power.
Discover this has only happened since an RCD incomer was installed 3 months ago.
Customer complains of RCD tripping when slamming door downstairs, turning light on upstairs or going into the study. It was discovered that each activity vibrated the landing floor.
A few board-lifts later....
The cable with sheath stripped back. Somehow the nail managed to damage the insulation to both live conductors. The cpc was "welded" to the line conductor having shorted and melted the pvc.