I have a supply to run in. It is a single phase 60A supply which is 135 meters long.
From my calculations, I'm going to need a 70mm² cable to keep volts drop within acceptable limits.
I'm trying to work out if it's going to be acceptable to use a 2 core cable, and rely on the armour only, or if a copper earth is required too.
I only need 14mm² of earth to satisfy the adiabatic equation, so I am well covered there, but I'm struggling to find the resistance per meter of steel to check my Zs is goint to be (a) low enough to provide ADS, and (b) low enough to supply final circuits and keep their Zs low enough.
From my calculations, I'm going to need a 70mm² cable to keep volts drop within acceptable limits.
I'm trying to work out if it's going to be acceptable to use a 2 core cable, and rely on the armour only, or if a copper earth is required too.
I only need 14mm² of earth to satisfy the adiabatic equation, so I am well covered there, but I'm struggling to find the resistance per meter of steel to check my Zs is goint to be (a) low enough to provide ADS, and (b) low enough to supply final circuits and keep their Zs low enough.