Swapped car charger for outdoor socket - reduce mcb rating?

Discussion in 'Electrics UK' started by garmcqui, 15 Nov 2018.

  1. garmcqui

    garmcqui

    Joined:
    20 Nov 2007
    Messages:
    245
    Thanks Received:
    3
    Location:
    Durham
    Country:
    United Kingdom
    i recently replaced my 7.2kw electric car charger with a 13a outdoor socket as we’re moving next week. The car charger had a 40A mcb fitted in the consumer unit and I am wondering if it is safe to leave it at 40A, or replace it with a 16A version?

    If it helps, the outdoor socket has a 16A rcbo built into it already.

    Cheers
     
  2. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    29,771
    Thanks Received:
    3,207
    Location:
    Retired to:
    Country:
    Portugal
    Yes, you can leave the 40A MCB in place - assuming 6mm² cable runs to the socket.

    What do you mean by the socket has a built-in 16A RCBO?
     
  3. flameport

    flameport

    Joined:
    10 Mar 2007
    Messages:
    8,230
    Thanks Received:
    1,511
    Location:
    Poole, Dorset
    Country:
    United Kingdom
    Presumably one of these:

    ROLEC.jpg

    The front can be changed to a variety of different sockets and connectors. Top half includes a suitable RCBO for EV charging.
     
    • Thanks Thanks x 2
  4. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    29,771
    Thanks Received:
    3,207
    Location:
    Retired to:
    Country:
    Portugal
    I thought he was talking about the replacement 13A socket.
     
  5. garmcqui

    garmcqui

    Joined:
    20 Nov 2007
    Messages:
    245
    Thanks Received:
    3
    Location:
    Durham
    Country:
    United Kingdom
    That photo is the exact outdoor socket I have put on in place of the electric car charger. It is a rather elaborate outdoor socket, but it fitted the same baseplate as the charger so avoided leaving holes in brick wall that buyer would want fixed.

    So due to the 16A rcbo being fitted (as pictured), the 40A mcb is ok to stay? (yes, the wiring is 6mm)
     
  6. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    29,771
    Thanks Received:
    3,207
    Location:
    Retired to:
    Country:
    Portugal
    Yes, it's fine.
     
    • Thanks Thanks x 1
  7. ban-all-sheds

    ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    69,785
    Thanks Received:
    2,857
    Location:
    London
    Country:
    United Kingdom
    If you did the latter you would need to apply for Building Regulations approval in advance.
     
  8. ban-all-sheds

    ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    69,785
    Thanks Received:
    2,857
    Location:
    London
    Country:
    United Kingdom
    Would they?

    Did they actually make that a condition of the sale?
     
  9. garmcqui

    garmcqui

    Joined:
    20 Nov 2007
    Messages:
    245
    Thanks Received:
    3
    Location:
    Durham
    Country:
    United Kingdom
    Their solicitor did, yes. Couldn’t believe it.
     
  10. AndyPRK

    AndyPRK

    Joined:
    4 Jan 2009
    Messages:
    4,354
    Thanks Received:
    387
    Location:
    Herefordshire
    Country:
    United Kingdom
    funky. How much does that entire enclosure cost?
     
  11. ban-all-sheds

    ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    69,785
    Thanks Received:
    2,857
    Location:
    London
    Country:
    United Kingdom
    • Thanks Thanks x 1
  12. AndyPRK

    AndyPRK

    Joined:
    4 Jan 2009
    Messages:
    4,354
    Thanks Received:
    387
    Location:
    Herefordshire
    Country:
    United Kingdom
    10A MCB is a little OTT


    I see they also do a socket and outside tap. Nice combo :rolleyes:

    I guess its for those with pressure washers
     
  13. 333rocky333

    333rocky333

    Joined:
    12 Jan 2008
    Messages:
    7,316
    Thanks Received:
    699
    Location:
    Essex
    Country:
    United Kingdom
    I assume the casing can be adapted for EV use as well as normal outdoor power, reading reg 722.55.101.0.201.1 it states a BS 1363-2 socket needs to be marked EV on its rear end if used for EV charging, whats the point of that.
    Is it just a warning that its connected to a type A Rcd
    I admit i am not too clued up on type A and type Ac Rcd's, but assume either Rcd type is suitable for a normal, non EV use as the Op has left it.
     
  14. 333rocky333

    333rocky333

    Joined:
    12 Jan 2008
    Messages:
    7,316
    Thanks Received:
    699
    Location:
    Essex
    Country:
    United Kingdom
    The 16 amp is irrelevant, the RCd side is important.
    The fact that the cable is rated for 40 Amp and the plugs will be 13a fused maximum is why the 40 amp Mcb can stay.
     
  15. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page