Thick liquid in switch

Joined
17 Feb 2004
Messages
700
Reaction score
1
Country
United Kingdom
While inspecting a property I opened a light switch, in it i found residuals of thick (green/blue) liquid like shampoo. I looked at the pull cord in the bathroom and it was the same, sticky thick subtense. I have left the site as did not agree with the customer but still would like to know, was there a time that this was used for any reason in or as I think that something is wrong there...?
 
Sponsored Links
Extract from IET forum

It is most prevalent in cables made between 1965 and 1971. The gunge is degraded di-isoctyl phthalate and is the result of the reaction between the plasticiser in the insulation and the copper. Between 1965 and 1971 the temperature performance of PVC was uprated by the inclusion of an anti-oxidant in to the PVC. An unappreciated side effect was that the anti-oxidant encouraged the production of exudate.

Evidence suggests that high ambient temperatures accelerate the process. The exudate is of low flammability and low toxicity. Although unsightly it does not reduce the electrical integrity of the conductor or the insulation.

Green exudate from PVC

Draft BCA statement (April 2001)

1) PVC

PVC comes in two main grades, plasticised and unplasticised PVC.

Unplasticised PVC (UPVC) is used for example in double glazing window frames where a rigid material is required.

The PVC used for manufacture of cables is a plasticised PVC that conforms to the relevant British Standard for the cable type in question.

2) Ageing effects

As a cable ages; (at temperatures above normal ambient), the elongation to break decreases (also the Insulation Resistance increases). The life expectancy of a cable is arbitrarily considered to be when the elongation to break of the PVC is 50%.
A lower elongation to break value could be considered suitable especially for a fixed wiring cable. Therefore, providing the cable is not subject to movement or when moved due to inspection of socket outlet or the like, the PVC does not crack, a much lower value of elongation to break is considered by some as suitable.

3) Greening

Greening is the appearance of a wet green substance that is a product of an adverse reaction between certain types of plasticiser and the copper conductors. This greening, which is a rare occurrence, can happen either after a long period of time for some cables, or if the cable has been severely overheated.
The plasticiser itself is a clear oily liquid that is non conductive. The green substance is a combination of copper oxide and plasticiser which may become conductive under certain adverse conditions.

4) Action if Greening is found

Therefore whenever this green substance is found at socket outlets etc. initially it should be removed and the terminations cleaned (gloves should be used) otherwise it is possible that tracking/overheating may occur. It is strongly recommended that rewiring should be carried out as soon as possible.


I found this on several properties recently so far no IR problems
 
Sponsored Links
Thanks for the replies, to the point and comprehensive
 