It is possible that you have a radial circuit rather than a ring final circuit. (Most sparks now prefer radial circuits to ring final circuits.) A radial circuit in 2.5 mm² T+E cable will usually have a 20A MCB (or a 15A fuse) whereas a ring final circuit in the same cable will usually have a 32A MCB (or a 30A fuse). IF you have a radial circuit then there is no limit to the number of spurs off spurs you are allowed because they are actually branches.
What is the MCB or fuse rated at on the circuit in question?
It is possible that you have a radial circuit rather than a ring final circuit. (Most sparks now prefer radial circuits to ring final circuits.) A radial circuit in 2.5 mm² T+E cable will usually have a 20A MCB (or a 15A fuse) whereas a ring final circuit in the same cable will usually have a 32A MCB (or a 30A fuse). IF you have a radial circuit then there is no limit to the number of spurs off spurs you are allowed because they are actually branches.