A 9.5Kw should be on 10mm cable with a 40A breaker or even a 32A if poss taking diversity into account.
6mm on a 50A breaker will have melted the cable as its undersized![]()
Using that shower on a 6mm is a fire risk!
Run a new 10mm cable from your consumer unit to the shower and downgrade the breaker.
It could happen in the extreme of adverse conditions, i.e. in conduit under/behind thermal insulation.Granted the cable is undersized, but how could a 41.3A shower melt 6mm² cable, rated at a maximum of 46A?
If the cable is already cooked then you're too late - replacing the shower won't eliminate the fire hazard.
yes there is a way. If you can't see it, pay me a thousand pounds and I will show you.
I'll show you for a mere £900.![]()
Wrong drill bits then.
Trunking?
You might be able to run it in ceiling space and then come down to the shower. Would that be any easier (you might still have to move tiles though)?
We have a length of trunking up the bathroom wall to the ceiling, then down the wall to the shower unit. Off-white tiles, so you dont notice it much. (We had to replace the cable a few years ago, since we bought a more powerful shower. The old cable was under the tiles and the bathroom is fully tiled, so trunking it had to be!)
Trunking goes into the top of the shower, sealed around it. Its not dangerous - all the cable entries are designed so that any water that enters them drains out of the bottom without going near any electrical components.
Is there any possibility that when you put the mirror up you may have caught a cable in the wall behind? Is there any correlation between the time the Mirror went up and the circuit tripping?
A photo of the inside of that switch when you get home should confirm this.
If the bathroom is only a few years old, the previous owner should have had an inspection, depending on the exact date of installation wrt when Part P came into effect, but then not everyone follows the rules.
Experienced people:
What chance do you think there is that I could get a 10mm cable up behind the tiles in the channel for the 6mm? Any chance I could pull the 6mm out bringing attached 10mm all the way through? Is this just crazy talk or can it often be done?
I had a hunch that it was.That tape measure photo is at the CU.
OK. That certainly appears to be a DP (double pole) switch. We really really REALLY need to know the gauge of the cable on both the supply and load sides of that switch, since there's no guarantee that the cable isn't joined somewhere between CU and DP switch.I don't have a photo of the red switch (I'm working today), but it's a lot like this one.
lol - no I didn't think you were. But if, for example, you have porcelain tiles, and if, for example, you were using ordinary masonry bits, then the bits would melt without cutting the porcelain very much.I wasn't using wood bits...
Yes, and oh dear, in that order.Will that look horrible? It's quite a nice bathroom.Trunking?
Not at all dangerous, but as ugly as sin on a bad hair day.I'm guessing there's probably no way to avoid removing at least a couple of tiles, either from the ceiling or floor. Trunking to the shower unit sounds dangerous and probably ugly as hell.
If I had a pound for every time I encounter that scenario, then I'd...... hang on - I do have a pound for every time.Since it would be so easy without the tiles it makes it even more ridiculous that they didn't do it properly in the first place...