Then you would have a 25mm² (round) tail and the (flat?) live feed to the RCD both crammed into the bottom of a BS EN60947-3 switch.
I am not sure they are really designed to do that. When you get to large conductors, one per terminal is the rule. That is why they invented Henley blocks.
Dear Sir, An extra neutral link can be supplied from the load side of the
main switch to feed this extra bar or as you say run the existing neutrals
from this bar to the supply side of each RCCB
They are referring to a 3rd cable to feed a 3rd neutral bar.
Ok so they're talking about tri-rated internal CU flexible cables, not 'tails but presumably if the terminal is large enough and done up tight enough and all cables are secure then it's not a problem?
However having 2 identical CU's side-by-side it could be confusing for the user that one big red switch only switched off that board whereas the other one switches off both boards. Obviously the real Main Switch should be labeled but could easily still be confusing.
To the OP - Order a 12-way from Screwfix, pay the extra delivery and be done with it? Inverness might be pretty remote from the main urban centres but it's hardly a backwater, I find it hard to believe that there are no wholesalers who have a 'board big enough. Also a good spark would have checked out how much space you have in your CU cupboard when doing the initial survey.
To the OP - Order a 12-way from Screwfix, pay the extra delivery and be done with it? Inverness might be pretty remote from the main urban centres but it's hardly a backwater, I find it hard to believe that there are no wholesalers who have a 'board big enough. Also a good spark would have checked out how much space you have in your CU cupboard when doing the initial survey.
I think he forgot about it as it's been a few months since we started work on the extension. They were supposed to come today, snowed in so has been postponed, and he rang last night. As it's going to be a while before I can arrange for them to come I will ask for a 12 way.
OK it says:- 537.1.4 A main linked switch or linked circuit-breaker shall be provided as near as practicable to the origin of every installation as a means of switching the supply on load and as a means of isolation.
A main switch intended for operation by ordinary persons, e.g. of a household or similar installation. shall interrupt both live conductors of a single-phase supply.
But in real terms two switches will do same job and the supply authority have to provide an isolator anyway as one is not allowed to work on live equipment so if the supply authority do their job right there is no need for separate isolator.
OK I know the supply authorities don't do what they should but it really is up to them not us to provide the first isolator.
An installation in this case would be a number of final circuits from a consumer unit. The main switch in that consumer unit would be at the origin and labelled as such.
Two consumer units supplied independently from a 100A henley block could well be seen as two installations, exactly in the way the ECS and the ECA (to my experience) see it.
I think maybe another reason for not managing to get a 12 way at short notice is that it needs to be an MEM unit. This is so that all our existing MCBs can be reused. I am going to see if I can find one in stock myself, what model MEM would be the one to get?
I think maybe another reason for not managing to get a 12 way at short notice is that it needs to be an MEM unit. This is so that all our existing MCBs can be reused. I am going to see if I can find one in stock myself, what model MEM would be the one to get?
MCBs cost a couple of quid each, so it isn't worth buying any particular brand in order to reuse what you already have. If he's not installing a dual RCD unit then he'll need to use at least some RCBOs as well, so your existing MCBs would be of no use anyway in that situation.
If you need to find a tradesperson to get your job done, please try our local search below,
or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Please select a service and enter a location to continue...
Are you a trade or supplier? You can create your listing free at DIYnot Local