    Hi,


    We are considering installing two 45A shower in a single property (multible showers). I believe the incoming service fuse is 100A.


    The problem is, if both showers plus other devices are used it could exceed the 100A max.


    Would it not matter as it's unlikely both showers used at the same time? I've seen one solution is installing a 'priority' board to prevent both being used at the same time, or a switch arrangement that performs the same function.


    Both showers would be on there own circuits with RCBOs.

    - -

    Is there any scope for additional mains supply, or would this be too expensive, potentially cause phasing issues, or non reg?

    Finally, if both showers were used at the same time could water pressure in an issue?

    Thanks in advance.
     
  2. Sponsored Links
  3. AndyPRK

    AndyPRK

    Joined:
    4 Jan 2009
    Messages:
    5,887
    Thanks Received:
    593
    Location:
    Herefordshire
    Country:
    United Kingdom
    If the fuse really is 100A, I wouldn't worry
     
    • Like Like x 1
  4. Taylortwocities

    Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    20,553
    Thanks Received:
    2,132
    Location:
    Oxfordshire
    Country:
    United Kingdom
    Yeah, what could possibly go wrong!

    Are you sure your supply is 100A?
    The service fuse cover may have 100A written on it, but that is the maximum fuse. Inside it may be 80 or 60A. Ask your DNO.
    100A is the max for a single phase domestic supply. To go larger, you would need to ask for perhaps a 3-phase supply, but that’s several thousands of pounds to install.

    Better, perhaps, to have one electric shower, and use the existing hot water supply, perhaps with a pump, to provide the second one.

    These sort of showers need mains water pressure and, of course, the pressure will halve if both showers are in use.
     
    • Like Like x 1
  5. jonpatterns

    jonpatterns

    Joined:
    29 Oct 2014
    Messages:
    8
    Thanks Received:
    0
    Location:
    Derby
    Country:
    United Kingdom
    100A supply fuse question IMG-20210126-01501.jpg 100A supply fuse question IMG-20210126-01501.jpg
    This is the power inlet. Does the 100A here refer to the fuse or max current for the unit?
     
  6. jonpatterns

    jonpatterns

    Joined:
    29 Oct 2014
    Messages:
    8
    Thanks Received:
    0
    Location:
    Derby
    Country:
    United Kingdom
    Thanks for the advice. Unfortunately, we are on electric heating, so may need to rethink. There is no gas supply currently to house. So maybe electric hotwater storage system and power showers?
     
  7. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    37,442
    Thanks Received:
    4,201
    Location:
    Retired to:
    Country:
    Portugal
    Max. current for unit.
     
  8. Sponsored Links
  9. ericmark

    ericmark

    Joined:
    27 Jan 2008
    Messages:
    18,616
    Thanks Received:
    1,746
    Location:
    Llanfair Caereinion, Nr Welshpool
    Country:
    United Kingdom
    That says the fuse holder will take up to a 100 amp fuse, that does not mean a 100 amp fuse is fitted.
     
  10. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    48,635
    Thanks Received:
    3,189
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    ... indeed, and that would seem to be perhaps the most obvious course for you, since it removes many of the questions and uncertainties.

    Kind Regards, John
     
  11. endecotp

    endecotp

    Joined:
    2 Dec 2013
    Messages:
    3,949
    Thanks Received:
    507
    Country:
    United Kingdom
    You can get relays that prevent both showers from being turned in at the same time.
     
  12. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    37,442
    Thanks Received:
    4,201
    Location:
    Retired to:
    Country:
    Portugal
    In a single dwelling, you can also decide, arrange and ensure not to use both at once; just like if you only had one shower.
     
  13. Taylortwocities

    Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    20,553
    Thanks Received:
    2,132
    Location:
    Oxfordshire
    Country:
    United Kingdom
    You haven't said where your hot water comes from at the moment, but you could install a largish unvented hot water cylinder and heat the water with an immersion heater, or two.
    You'll then get hot water showers at mains water pressure.
     
  14. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page