I've check and unjammed the pump, so that's pumping fine. I've flushed all the UFH pipes, so they're primed and not blocked. I've checked all the motorised valves, and they all appear to activate: you can hear/see them switch as expected. I've also looked at the mixing valve (where the hot feed and cold feed mix so the UFH doesn't get too hot): if you set it to fully cold the flow through the UFH pipes is good, but setting it to anything warmer than that means gives no flow at all. I've swapped out the mixing valve (as I have no way to prove it works) with a spare I've had in the loft for a while (which I'm assuming works). But I'm still getting the same response.
Yes I have bled the system and there is heat in the radiators so I know there is heat available to get into the UFH system. I have also checked the flow pipe to the manifold, and that is supplying water.
When I have it all connected up and turned on, I'm getting water out of both bleeding valves.
It could be as simple as my spare mixing valve is also broken, but I don't want to spend £130 unless I have to.
Yes I have bled the system and there is heat in the radiators so I know there is heat available to get into the UFH system. I have also checked the flow pipe to the manifold, and that is supplying water.
When I have it all connected up and turned on, I'm getting water out of both bleeding valves.
It could be as simple as my spare mixing valve is also broken, but I don't want to spend £130 unless I have to.