By virtue of what might perhaps be regarded as some degree of foresight many years ago, I have a run of about 25m of ~100mm plastic conduit encased in concrete buried (about 800mm depth, if I recall) in part of my garden. One end enters the cellar of the house and the other emerges in a garden building (dare I say 'shed'?!). Currently it only carries some small SELV 'signal' cables.
I am contemplating the possibility of running a power cable through it. I would have thought that concrete-encased conduit probably satisfies the qualification of 522.8.10 regarding "equivalent [to armour] protection against mechanical damage", in which case I could probably theoretically use ordinary T&E cable. What do people think? Admittedly, the price differential between T&E and SWA is fairly small (less than 2:1), but in these hard financial times, I guess that 'every penny counts'!
Kind Regards, John.
I am contemplating the possibility of running a power cable through it. I would have thought that concrete-encased conduit probably satisfies the qualification of 522.8.10 regarding "equivalent [to armour] protection against mechanical damage", in which case I could probably theoretically use ordinary T&E cable. What do people think? Admittedly, the price differential between T&E and SWA is fairly small (less than 2:1), but in these hard financial times, I guess that 'every penny counts'!