    want to upgrade shower from 8.5kw to 10.5kw is that ok ? what to look out for re electrics
     
    Last edited: 2 Jun 2020
  2. denso13

    denso13

    Joined:
    22 Jan 2007
    Messages:
    4,003
    Thanks Received:
    904
    Country:
    United Kingdom
    Probably better in the electrics forum but cable size, route and rcd/mcb/rcbo requirements are but a few.
     
  3. Sponsored Links
  4. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    34,581
    Thanks Received:
    3,833
    Location:
    Retired to:
    Country:
    Portugal
    You will need a 45A or 50A over-current device plus RCD, and

    depending on the cable installation method, 6mm² or 10mm².
     
  5. Taylortwocities

    Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    19,765
    Thanks Received:
    2,019
    Location:
    Oxfordshire
    Country:
    United Kingdom
    What do you have installed for this circuit?
     