- Joined
- 17 Oct 2021
- Messages
- 4
- Reaction score
- 1
- Country
Hi DIYnot,
Firstly, i will apologize beforehand as my english is not perfect. I am from Denmark, seeking some guidance as i haven't managed to find a plumber or a boiler technician who can help me with my problem.
I have had a bigger renovation project where i switched from radiators as a primary heating source over to pure floor heating.
When heating demand required, the flame turns on for only 10 seconds and then shuts off. I have had several plumbers and boiler technicians over, but nobody seem to have the knowledge of the issue. I have had a talk with Danfoss which advise me to add a automatic bypass valve, but i really don't know if it helps.
I have added a diagram of the installation together with a video of current situation.
https://imgur.com/a/PFcZsOF
Can somebody guide me?
Both circulation pumps are running.
Vaillant EcoTEC Exclusive
VC206
D0: 4 kW
D2: 5 minutes
D40: 40
D41: 30
Minimum temp. 30°C
Max. Temp. 50°C
Pump pressure: 250mbar
Differential pressure: 170 mbar
Flow: 650 l/h
Floor heating
Fully balanced system
9 circuits
480m in total length
Design
Heating demand: 3955 W = 4kW
Flow: 426 l/h
Pump pressure: 0,042 bar
Supply temp. 42,1 °C
Delta T: 8°C
VC206
D0: 4 kW
D2: 5 minutes
D40: 40
D41: 30
Minimum temp. 30°C
Max. Temp. 50°C
Flow: 650 l/h
Floor heating
9 circuits
Design
Flow: 426 l/h
Delta T: 8°C