Sorry I missed this earlier, although it does cause issues occasionally in the domestic situation, correctly applied diversity is usually not a problem. Here at home we have an 11.2KW ceramic top cooker, when I installed it I had to extend the feed and to get the job done in a hurry I put a piece of 2.5mm² T&E in temporarily and as I had a 25A MCB handy I used it, diversity comes out at ~22A. A couple of days later I replaced the temporary T&E. Some 10 or so years later it tripped when every element was in use, by then I'd made a 32A MCB spare and changed it over quickly, the only other time it tripped was a faulty element after I'd changed to RCBO and that was I suspect on RCD action.From what im rrading this seems to be a bone of contention amoungst electricians even though the regs seem to support it.
For i just want to be sure that if i turn on teo ovens at 200c and have two maybe 3 things on the go on the hob at the same time it wont trip. This for me would be worst case "Xmas Day" scenario.
As it stands oir electrician is saying no possible which means we would have to move where we want the ovens on the island under the hob to another location in the kitchen which quite frankly looks naff.
I imagine running your appliances on 32A will be fine unless you do mega catering, If your cable is 6mm² it might be acceptable to upgrade to 40A (your electrician should be able to assess your installation) and that should cater for a 25KW set-up.
The thing that should be done is follow instructions regards to 16A MCB for the ovens as the wiring will be too small for 32A MCB.