What size and make of boiler ?
9 Oct 2009
Bristol
Hi all,
I have a 5-bed, 4-bath house (1 master, 3 en-suite) plus a downstairs WC. It’s 270 sqm with 19 radiators. When the boiler was first fitted the house was 210 sqm, but was extended about 3 years ago and we bought it 16 months ago.
The boiler is an 8-year-old Vaillant Ecofit Pure 630 (30 kW). It’s always struggled to get heat to the last two radiators on the circuit. Most rads don’t have TRVs, and I assumed fitting them might help by pushing flow to the end of the system and perhaps a system clean.
Recently the boiler has started making noise. I suspect it needs cleaning, flushing and inhibitor, though there may also be a mechanical issue.
Online guidance seems to suggest a suitable replacement is a Vaillant EcoTEC Plus 35 kW or Worcester Bosch 8000+. I know calculators aren’t perfect compared to a proper survey, but does it sound like I need a larger boiler, or is the current one likely correctly sized and just in need of proper maintenance?
Sounds like you need to get radiators balanced.
You also need water inside to be clean with inhibitor.
Find a good local heating company to come and advise.
Oh. You can get booster pumps
It also probably depends on how well the house in insulated. When was it built.
Are you able to increase the power on the pump.
I did do that about 9 months or so ago and worked to balance out the rads as suggested above, it seemed to be better in October but haven't had guests stay overnight in December. Been more distracted by the noise of the boiler which is somewhat noisy !
What temperature is your room stat set to maintain, during the night?
The TRVs where we have them upstairs are normally on 3 i.e roughly 20c, we normally set upstairs to 20c until about 7pm and then leave it off apart from a little 30-40 min kick at 2am. That's when outside is approx 10c as it is now.
The house also has 2 zones for upstairs and downstairs central heating, so we don't really heat downstairs past 8.30/9pm unless it's very cold outside and downstairs is all TRVd.
I do normally try to heat downstairs separately to downstairs to boost performance, as we also have a 300L unvented cylinder and the heating performance drops when both upstairs and downstairs are on, then another knock when the water cylinder is being heated.
You didn't answer the question - what is your room stat temperature set to, during the night hours?
Mine is set to 14C, and it is extremely rare, for the indoor temperature to fall that low, during the night.
Oh I see, it's 10c, i.e basically don't activate unless I have it set at 20c at the stated times. It will never get lower than 17/18, after I run the previously mentioned schedule.
It really does sound like a distribution of heat problem, ie balancing.
You didn't say where these two 'rads at the end of the circuit' are located - in the downstairs extension?
Is the extra 60m2 of floor space downstairs only?
I will guess at 5 rads in the bedrooms, four rads (towel rails?) in the bathrooms, and 10 rads downstairs.
I suggest the following actions:
1. Make sure the system water is clean, by flushing or otherwise.
2. Make sure the pump is clear of debris....dismantle, inspect, clean.
3. Close off all towel rails, then inspect the 'cool' rads for proper heat output (Do they now get hot?)
4. If not measure your gas rate at the meter...take a reading every 30 seconds over a 5 minute period with only the boiler running and on CH only.
Are all readings similar, and are they the same as readings taken with a cold system initially?
If the gas rate drops off on a 'hot' system then your boiler has power to spare (it's modulating the flame, and therefore the gas rate, down).
I have had previous problems with Vaillant heat exchangers furring up with a type of scale that is hard to shift. The result is a loss of heat output as seen with the gas rate monitoring. The solution was to fit a new heat exchanger, though this may not be your solution. Others may be willing to suggest a product with which to flush out this hard scale.
MM
This seems to be the pump curve from the manual. Although it looks like the axes are labelled the wrong way round in the notes underneath. Your boiler seems to have a variable speed pump, where the default setting is that the pump speed is linked to the boiler output at any given time.
If the OP has a smart meter, and an indoor display, the display will be able to indicate the instantaneous gas consumption, in Kw.
My boiler 20 kW also 5 bedrooms, and it is ample. But I have TRV's on all radiators, 10 with electronic heads, 4 still with mechanical heads, and we found the main problem was the single thermostat in the hall was not calling for heat when required as the hall cooled too slowly, adding extra thermostats which could fire the boiler was all it needed.
MM
The two rads are in a previous extension which contains the 5th bedroom and ensuite. The rest of the additional space is downstairs in a large open plan area.
6 rads across five bedrooms, 5 towel rails across five bathrooms and one toilet, 1 upstairs hallway, 1 upstairs walk in wardrobe, Then 1 in downstairs utility, 2 upstanding rads and 1 in open plan area, 1 normal in downstairs office, 1 upstanding in hallway, 1 in front reception room. So actually 20 rads.
1. Thanks I will
2. Ok
3. They do get fully hot, they just take quite a while to get there
4. Thank you will do this
