Does anyone know how accurate the AI response is?
Like most AI created gubbins, it's based on various elements of truth, but those are taken from different sources and different time periods, so when combined the result is a confused jumble of ideas with no context.
A long time ago, fuses in plugs were rated to the flex attached, which was directly related to the power requirements of the device at the end of the flex.
3,5,13 were the usual values and were suggested for a whole range of different appliances. 3A for the side lamp, 5A vacuum cleaners and fridges, 13A for ye olde 3 bar electric fire and so on.
Other ratings existed for various specific purposes such as 7 or 10 for office furniture which contained electrical outlets.
All very well and desirable when the circuit contained a 3036 rewireable fuse, which even if it did contain the correct fusewire would be so slow to react, any appliance flex would be on fire without local protection.
Today, the vast majority are either 13A or 3A, the flex on certain items like kettles is routinely undersized due to the intermittent nature of such loads, and fused plugs in general are mostly irrelevant.
With modern circuit breakers, most short circuit faults will cause the 32A breaker to disconnect before the fuse fails.
Overload is mostly irrelevant with a single item attached.
2 way adaptor cubes typically are unfused, so no help there.
3 way types are usually fused, but attaching 3 items to overload and open a 13A fuse would require a special effort of 3 modern electric heaters on full in a room which was at sub zero temperatures.
That only leaves multi way extension leads, where the fuse could theoretically provide some protection against overload, but in reality this rarely happens as 13A fuses require a very substantial long term sustained current to open on overload, and in most cases the plugs/adaptors melt long before the fuse opens. Also see a sub-plot regarding the poor standards of education and social understanding where many people are entirely unaware of what fuses are actually for and would probably just replace the fuse when it failed rather than consider why.
Other niche uses such as 3A FCUs for gas heating systems are mostly based in ancient traditions rather than actual engineering, and would be far better served by having dedicated circuits for such things.