Will my tumble dryer be safe?
Probably ok? it depends. The instructions for many tumble dryer tell you not to use an extension reel. Here’s why:
Current draw of the dryer. The draw of the average tumble dryer is 11amps.
.... Now look at the rating of your extension lead. Example below. Fully wound it can only hack 3amps. Unwound it may not be able to handle the tumble dryer.
So care needed. Make sure your extension reel can do 13amp. As John has pointed out.
Indeed - but did you not read the post of mine which you quoted (and to which you are responding), in which I wrote:
If it's fully unwound, rated at 13A and serving nothing else at the same time as the dryer, that's probably OK, even if not ideal.
Kind Regards, John
Yes, I was trying hard not to dis your post, because I know that you would jump on any hint of opposing input.
That is why i was careful to add (at the bottom)
Yes, if you had questioned or criticised me for saying that one needed to make sure that the reel could take 13A, then I definitely would have 'jumped on you' :)
To be honest, I missed that. Thanks.
Kind Regards, John
Okay thank you - assuming the electrician who is upgrading the fuse box today could do that if I ask, fingers crossed
If he can't do it, I would question whether he really was a (competent) 'electrician'.
Kind Regards, John
I would not expect there to be a problem with the squashed cable, but clearly one can't be sure, and really no way to test without damaging the cable. But an insulation resistance test would satisfy me. As long as correct fuse/MCB fitted and RCD protected I can't see much of a problem.
As to tumble drier on an extension, for a resistive heater type, they use a lot of power, often over 2 kW for an extended time, and there is a question as to if should be on a dedicated supply anyway, although often they are not, the only item in the house below 3 kW which is likely to over heat a supply more is the immersion heater, but we all including myself tend to cross our fingers and trust to the Lord, and worse case scenario seems to be blown fuse or tripped overload.
However with a heat pump type the scenario is very different. It uses less power, and also cycles on/off, so unlikely to ever cause a fuse to blow or a overload to trip, except for any overload built into the unit. The problem with any refrigeration plant running on single phase is the time it takes to start, and the time it takes to build up pressure, the motor needs to reach run speed before the pressure increases to a point where it can stall the motor, a internal overload is included and if this trips on the odd time, when for example the unit is unplugged then plugged back in before the pressure has dropped, then the internal overload will do its job and turn the unit off, then back on latter when it has cooled and the pressure has also dropped. However if this happens repeatedly then the overloads often burn out.
So volt drop on refrigeration units is important, near every freezer states do not use extension leads as a result, it seems to be a standard entry in the users manual, even with inverter models which have three phase motors so really no problem, or at least not until the volt drop is huge. The inverter reduces the inrush and compensates for volt drop, so not really a problem, the one item I found the problem with was AC units used in porta cabins, which used more power than a domestic fridge.
I have no idea what is inside the heat pump tumble drier, it may have an inverter, but I simply don't know, I know it dries my cloths, and uses less electric, and I would use as short as an extension as I could and as heavy of an extension as I could, and nothing else on same extension, since the motor switches on/off so often I don't think I would know if it tripped the built in overload, to be frank I have never sat and watched it. I switch it on, and return when I hear no noise. Most items out of interest I have used an energy monitor with, but never bothered with the tumble drier.