    So I must have tempted fate buying a Nest system to have installed, because before it as been done I have noticed a problem with my combi.

    Once in a blue moon I have to use the key to top up the system (maybe once every 12 months or so) and the other day it looked to be low so today went to top it up. But after opening the plastic nut to let some water in, I noticed after a few seconds that the gauge wasn't moving. It is stuck at just very slightly below 1.

    I figured there was an issue, so put everything back and stuck the heating on to see if it was working ok - which it is. But I have no idea what pressure the system is currently at, and also noticed the overflow pipe outside has a very slow drip. And I mean slow....like drip...…...drip...…..drip :)

    Is there a way for me to drain some water of easily? Is it an easy job to replace the pressure gauge? I have checked out prices and they are cheap enough, but I know that I can't just undo this old one without flooding my kitchen. Is there a shortcut for replacing the gauge? Like some kind of stop next to it? Or am I asking too much for that to be a thing?

    Thanks very much for any advice.
     
  2. ianmcd

    ianmcd

    Joined:
    15 Aug 2010
    Messages:
    9,099
    Thanks Received:
    2,470
    Location:
    Lanarkshire
    Country:
    United Kingdom
    your pressure guage problem is absolutely nothing to do with the nest installation, topping up the pressure once a year is perfectly normal, the gauge is probably fine but will be blocked where the capillary tube joins the boiler drain the boiler and remove it and have a look , easiest way to lower the pressure for an amateur is open a bleed point at a convenient radiator and catch the water coming out into a bowl or pot till you have reduced the pressure
     
    • Thanks Thanks x 1
  3. Retro_uk

    Retro_uk

    Joined:
    Friday
    Messages:
    6
    Thanks Received:
    0
    Country:
    United Kingdom
    Ok thanks. And yeah I knew it was nothing to do with the Nest, I was just saying that basically it was sods law :)
     
  4. ianmcd

    ianmcd

    Joined:
    15 Aug 2010
    Messages:
    9,099
    Thanks Received:
    2,470
    Location:
    Lanarkshire
    Country:
    United Kingdom
    you will see when you remove the capillary tube, the waterways is tiny and any amount of crud will block it
     
    • Thanks Thanks x 1
  5. Stadan20

    Stadan20

    Joined:
    21 Sep 2015
    Messages:
    1,971
    Thanks Received:
    211
    Country:
    United Kingdom
    But chances are that you have overpressurised the boiler as gauge is not giving a reading , which has resulted in the prv to activate ( hence drip outside ) chances are that prv will also need replacing
     
    • Thanks Thanks x 1