If they were early enough to have numbers they'd have been Type 1's - even more frisky than Bs, they trip if you so much as look at them sideways...fireman22 said:i thought early ones were type 2 or 1 or something who`s curve may have been better
mapj1 said:Why not use type C in certain domestic situations - would you fit a 16A B type to a radial for a freezer - fie on you if you would - the risk of nuiscence tripping is too high, and there is no condition in which the 13A fuse is worth having.
A typical PC or TV has a 70-100A inrush so it is reasonable if its on a 32A ring (B type, 70-150A surge allowed) so it makes sense to allow the same on a radial 16A C type (also 70 -150A surge allowed) if false tripping trouble is to be avoided. On lighting circuits , as the clearing time is 5 seconds, not 0.4, unless the wiring is so long the earth impedance cant be met, a C6 is a sight safer than a B10, on 1mm wiring.
I agree sprinkling Ctypes willy nilly is not good, but there are many situations where they are exactly what is required.