Position of consumer unit

Joined
17 Jun 2009
Messages
75
Reaction score
0
Country
United Kingdom
I've recently wired for a CU at a house but then when i went back to the house the builder told me the kitchen plan had changed and that the sink was closer to the CU that i had expected. It is still 1metre from the nearest edge of the sink to the nearest edge of the CU. Is this still allowed?
 
yes, from the rinse board/sink/ nearest water tap you have to allow 300mm, but i would not reccomend putting your c/u 300mm from the water supply. also will the c/u be protected ie boxed in?
 