What is the rating of the cable as installed? I'm thinking a multicore in conduit is Method B which from table 4D2A (4D5 doesn't have a column for method B) has a rating of 38A which therefore not suitable for a 40A MCB.
Is that size cable rated for the load that will be on it, given its installation method?The cable will be 6mm T&E.
That might be more than the cable rating.A 40A MCB is required to protect the cable as it needs to be less than the cable rating.
Earthed conduit?No RCD is needed because the cable is protected by the conduit.
I can't answer that, but you have suggested that it isn't so I will query it.Is that size cable rated for the load that will be on it, given its installation method?
The manual is here. I can't find any numbers in there but the company I bought it through provided instructions that showed positions, ratings, and so on and it did show a 45A DP switch. However over the phone the manufacturer said that a 45A circuit would be fine. I will query with the electrician if they meant 'up to' or 'minimum'. I was present when he called them but I didn't hear the whole conversation.But the biggest problem is that the installation instructions for the cooker tell you to provide a 45A supply, not a 40A one, so your proposal will not comply with the instructions and therefore will not comply with the wiring regulations, so if your electrician signs an EIC for it it will be false, and therefore so will his declaration that the work complies with the Building Regulations.
That's why I'm asking.There is absolutely no excuse for not doing it properly.
I understand the reasons why from these replies and I will pass those on. If the cable is changed to 10mm/2 would the breaker not still need to be less than 45A because the isolator switch in the kitchen is rated at 45A? Or is that wrong as well?Do not use a 40A breaker, and do not use 6mm² cable.
Yes to all three. Fortunately that much I do understand. It's when numbers and ratings come along that my eyes glaze over.Earthed conduit?
Over its entire length?
No socket on the CCU?
Seriously - if you've got an electrician who thinks that 6mm² cable is OK for a 45A circuit then it's time for you to get a new one.He has said that he calculated that 6mm cable would be ok
As they specified 45A that is what he has designed it for...
http://www.diynot.com/forums/viewtopic.php?p=76467#76467Does this sound reasonable? Is it true that circuit breakers only trip at over three times the rated current? That sounds a bit dangeous to me (120A needed to trip a 40A breaker?)![]()