You missed two:So what would be the difference between a qualified person and a keen diy'er to fit an outdoor socket here be?
Ok a botch job by a diy'er might include
Adding an outdoor socket to a unsuitable existing socket
Loose connection when adding the extra cable to the existing socket or insulator rammed into the terminal connectors,
cable overstripped/understripped, bending the cable and maneuvering it in awkward ways which might weaken it
Inappropriate parts used or not used (cable size, enclosure boxes, sockets, cable glands etc)
Choc blocks wrapped in insulation tape![]()
Burying normal cable in the lawn
Fitting the socket next to the outside tap
Hi thanks for the advice mate.
Yes, directly from existing socket.
I will also take your advice then, so I'll get a FCU, what cable should I run from the existing socket to a FCU then?
You can use 2.5mmsq T+E for your short spur from the nearby indoor socket to the FCU supply terminals, also indoors. From the FCU load side terminals you can use your 1.5mmsq HiTuf.
I might even think about putting the FCU in the garage, and running another cable out from garage to pond equipment.
I'm not sure that would work. The FCU is there as you're only allowed one unfused spur from any point on a ring final circuit, be it a double socket, FCU, single socket, or any other electrical accessory. If you spur from the indoor socket to the outdoor, and also to an FCU in the garage feeding another outdoor socket, that's more than one accessory being fed by an unfused spur.
Why not go indoor socket > 2.5mm T+E > FCU supply > FCU load > 1.5mm HiTuf > garage socket > 1.5mm HiTuf > Pond socket, thus alleviating the need for a JB?
No I wasn't planning on burying this stuff, it's going to run about 100mm above ground, is this ok? Or should I use conduit anyways?
Nah, that should be fine, it'll take a fair bit of hammer to damage HiTuf. It's fun enough to strip with a sharp knife, never mind garden tools.
T&E is not suitable for use underground, whether in conduit or not.by the way, I'll need to use conduit because the 2.5mm T+E needs to go underground (
Rhetorical question of course Rice.
Of course he doesnt even think about testing. Or Part P. As long as it works when he switches it on it must be OK.
Trouble with these sites - on the one hand at least people are asking for help and might take notice of advice given on the other hand it purely encourages more DIY bodges.
There is no problem with the short unfused spur, it just makes more sense to avoid it given the chance.
Unfortunately you cannot feed your FCU from the two sockets you mention that are already unfused spurs from the ring, as an unfused spur is only permitted to feed one accessory.