Can any one suggest a reason why my Remeha comby cannot supply hot water at the correct temp anymore - its seems to try and goes luke warm. The central heating works fine!!
1. Any Error (E) numbers on the display? No
2. What sequence of numbers do you get when the HW is turned on? 3
3. Which number is displayed when the water goes cold? 3
4. What is the t1, t2 and t3 temperature? (Press the + key to display t1 followed by a number - that's the temperature. Press + again for t2 and t3)
I looked at these and the temp starts to rise initially upto 65 and then falls back down. Seems to be flow related to a certain extent.
5. What external controls do you have? A standard thermostat and 7 day controller
Scaled plate HE or Thermistor fault neither of these will bring up a code every time![]()
There are 2 thermistors, one on the boiler flow, the other on the return (behind the fan)
I personally do not descale Plate HE's (some on here do though!)![]()
When HW is called the sequence should be 0, 1, 2, 4.2. What sequence of numbers do you get when the HW is turned on? 3
Then it's back to a blocked heat exchanger.Sorry I remembered it incorrectly - it is showing 4 for HW and 3 for CH.
Ask Remeha for their recommendations on in-line anti-scale devices.Yes I do unfortunately....
what else should I be wary of?