Most manufacturers state, well we do, that a boiler output of over 18kw should have 28mm primaries from boiler.
No you do, most don't.
No tony not necessarily should the boiler be 28mm pipe!
It all depends on available pump head and system design velocity!
Noise.Why does flow velocity matter in the pipes between boiler and motorised valves? It's below 1.5 m/s in both size of pipe.
The head loss in a 22mm pipe (flow and return) will be only 0.8m. So there should be enough head left to pump the water through the rads.
See this on a daily basis whereby circulator head is an issue , easy way out is to install a secondary circulator in series with the existing boiler circulator , job done.
Agreed. I calculated it, as a worst case, from information given earlier in this topic.That will be dependant upon loading/tube length/diameter.The head loss in a 22mm pipe (flow and return) will be only 0.8m. So there should be enough head left to pump the water through the rads.