A switch drop/fan supply is different because you can only see the cores at the terminations, where it's over sleeved. A bonding cable you can see the colour throughout the length of the cable.
That's true, but riveralt was throwing at me a regulation which applies as much to switch drops etc. as it does to bonding conductors.A switch drop/fan supply is different because you can only see the cores at the terminations, where it's over sleeved. A bonding cable you can see the colour throughout the length of the cable.
That's correct. Well, the first bit is only true, per regs, of a G/Y single. As often discussed (often in the context of plumbers!) it is strictly not in violation of the regs to over-sleeve the ends of the G/Y core of flex to use it as a live conductor - even though it is an 'orrible practice!From my reading you can't use green/yellow for anything but earth, however the reverse is not true, ...
Hmmm - I'm really not sure that it is sensible to call a bonding conductor an extraneous-c-p. If you did, then you would then presumably create a vicious circle which would require you to install an infinite number of bonding conductors - since each such conductor you installed would itself then need to be bonded... since the cable is a extraneous-conductive-part it is under 514.6.1 exempt from colour markings.
Such labels are only required at the ends of the conductor - and, in the OP's case, I suspect that they would both be indoors.But I would say in that case 514.13.1 would come in so labels stating "Safety Electrical Connection - Do Not Remove" would need using, and on balance I think a green and yellow cable would be better than the labels.
Hmm again! I've already mentioned that, but I'm not convinced that black paint is materially different from black insulation or sheath!If it were me I would use green/yellow then paint it.
That discussion most often seems to arise in relation to cables connected to heating 'wiring centres', which invariably get a CPC from some other cable, but that doesn't necessarily get them off the hook as regards a CPC for whatever is at the other end of the flex! I've personally most often seen (albeit not very often) over-sleeved (or not over-sleeved!) G/Ys used as live conductors in cables to room thermostats and timer fans.Although the applications where you could have a flex or cable in fixed wiring which didn't require a cpc anyway are pretty limited, and most plumbing isn't one of them!As often discussed (often in the context of plumbers!) it is strictly not in violation of the regs to over-sleeve the ends of the G/Y core of flex to use it as a live conductor - even though it is an 'orrible practice!
I don't doubt it. As I've shown before, they use a red-insulated (albeit brown-sheathed) conductor to bring the neutral of my overhead supply into my houseIm sure the Dno use black cable as earth wires sometimes
That's what I do when running PEB's outside.Why don't you run it in some black conduit ?
DS
I think he only said that because he thought there would be a requirement for it to be G/Y indoors. If he decided to go with his black or brown cable (without conduit), with G/Y identification sleeving at ends, then he could presumably have an unbroken run of his black or brown cable.The thing that bothers me is the OP talks about running part of the cable in another colour which implies it will be jointed.
Indeed.In a 3 core SWA cable it was perfectly acceptable to use the yellow as the earth if sleeved with a trace of green and yellow. With that in mind, it's now acceptable to use the black of an SWA as the earth, again with a short sleeve over it. With that in mind, the grey or even blue (if 4 core) could therefore be used.
Indeed. As I've said, the concerns seem a little over-cautious to me - and I think that any colour with G/Y sleeving at ends would be reg-compliant.With that in mind, I SUPPOSE a black or grey 10mm2 single insulated single core COULD be used for the bonding.
It's not really at the ends that there are any concerns. It will be fairly obvious what it is, and that it is 'connected to something' (with a 'do not remove' label at least at the extraaneous-c-p end), so I don't think that more than a token bit of 'identifying' G/Y sleeving at the ends would really be necessary. People's concerns related to the black/brown/whatever cable being cut in the middle, "because it didn't light up a volt stick".I would insist on a generous amount of large green and yellow sleeving (not tape, bit rubbish) at the ends where the cable is terminated.
In a sense my 'first reaction' feeling is the same, but the more I think about it, the less I regard it as a cause for concern.Doesn't feel quite right though, so I'd like opinions on this.
Yes, I mentioned that a couple of posts back - and I agree that we decided exactly as you say.Conversely, I think the forum did decide it was ok with say a 3 core flex, it WAS OK to use the green and yellow core as a live conductor IF sleeved correctly, and IF the accessory had another form of earth point at it. We also decided it was NOT OK to ever use a bare earth wire in a T&E cable as a live conductor.