Yeah I realise what I actually wrote was a bit unclear/ambiguous, but that's why in the clarification I quoted the two words "they" in bold to illustrate that its the same they I was referring to. If you go to that post and look at the two quotes with the bold word it should make more sense.Apologies. I must be getting old, since I still don't really get what this "they" was meant to refer to, given that the neutrals of two circuits on different RCDs will, of course, go to different places (and hence are not 'the same neutral'). To remind you, you wrote:
In general yes, but it's the balance issue again, the MCB should be protecting both the line and neutral for overload. A lighting circuit with an extra light isn't going to be a problem but imagine the extreme case where the shower circuit is borrowing the lighting circuit neutral. The 1mm neutral isn't going to last long.As I wrote in the previous post, it has 'topological' meaning (the neutrals travel in different cables) but is electrically meaningless, since they are joined at a neutral bar in the CU.
We're on the same page now, this is exactly what I'm getting at.If they come from sparate MCBs, then you would have two lines so should have two neutrals and should not swap them.
Right, I think I've got it now, and I think I understand why I have been talking at cross-purposes with some of you ...By "They" I took it to mean the N to the first floor lights AND the N to the passage light, the OP was trying to get confirmation THEY were on the SAME circuit and not a borrowed neutral, ... The op was concerned that he did not want to connect his new gizmo to the 1st floor switch and the N to the passage light without confirming the passage N was NOT connected to the Ground floor lights
What he is unwilling to do is to admit that he made a mistake - he misinterpreted what John D said, and now he will not back down.I don't teach 'electrical knowledge', but what you wrote made absolutely no sense to me, and you seem unable or unwilling to explain to me what you meant.I'll give you one bit of advice, improve your teaching of electrical knowledge and don't get so uppity when your protoge is criticised for being wrong.
Sure - but, needless to say, I was thinking and writing about the only context in which this situation - i.e. two lighting circuits (both with over-engineered cable sizes!).In general yes, but it's the balance issue again, the MCB should be protecting both the line and neutral for overload. A lighting circuit with an extra light isn't going to be a problem but imagine the extreme case where the shower circuit is borrowing the lighting circuit neutral. The 1mm neutral isn't going to last long.
Yes, I've got it now. Thanks for your patience.Yeah I realise what I actually wrote was a bit unclear/ambiguous, but that's why in the clarification I quoted the two words "they" in bold to illustrate that its the same they I was referring to. If you go to that post and look at the two quotes with the bold word it should make more sense.
Well, just very bad practice, I suppose.We're on the same page now, this is exactly what I'm getting at.
Would you mind explaining exactly why you shouldn't swap them?
Remember it's 2 MCBs with no separate RCD protection and the neutrals only run to the switch and on to their respective light fittings.
IF those neutrals both came straight from the CU and went nowhere other than to their one respective light, then I don't think there would be any problems swapping them (the two feeds from the CU would be effectively interchangeable). However, if there are other loads connected to either of the neutrals, then EFLI's diagram could come into play (IF one cut some part of the neutral path)..... Would you mind explaining exactly why you shouldn't swap them? ...
That may be electrically true but from a safety point of view, very careless and potentially dangerous when working in the CU.IF those neutrals both came straight from the CU and went nowhere other than to their one respective light, then I don't think there would be any problems swapping them (the two feeds from the CU would be effectively interchangeable).
Then, why do it?However, if there are other loads connected to either of the neutrals, then EFLI's diagram could come into play (IF one cut some part of the neutral path).
So don't do it.Furthermore, as I have said before, there is, as far as I can see, no problem with intact circuits - since 'swapping' two conductors which come from the same bar in the CU means nothing. The potential problem/danger arises if there are multiple loads and one breaks the neutral path at some point.
JohnD introduced this hypothetical offshoot of the discussion by talking about singles. In that context (and in the 'single loads' scenario I mentioned), about the only meaning that 'swapping' has is in relation to which terminals of the (same) neutral neutral bar they are terminated into - is that what you mean>That may be electrically true but from a safety point of view, very careless and potentially dangerous when working in the CU.
I wouldn't. Even if I did (by accident), it's pretty likely that a RCD or two would bring the 'accident' to my attention.Why would you (not one) do it other than by accident?
What is a silly argument? - JohnD's hypothetical question? I hope you don't think that either he or I are advocating deliberately installing 'borrowed neutrals', or suggesting that anyone should deliberately install them today, do you?So don't do it. It's a silly argument.
Do you have RCDs in your consumer unit? Are the lighting circuits on different RCDs? If yes to both, then they are the same neutral.
sometimes the landing light if it has 2 way switching is on the downstairs live and upstairs neutral, but that wouldn't cause you an issue.