Twas the legend on the sticker
That is correct, but for domestic installations and the majority of others, PME = TN-C-S.PME is surely relating to the network and not the earthing system presented at the service head.
Indeed** - and I have to say that I was very surprised and disillusioned when the late-lamented westie told us (presumably correctly) that, at least for domestic distribution, the 'M' of PME often meant just one extra earth - one at the very end of the distribution cable in addition to the one at the transformer!That is correct, but for domestic installations and the majority of others, PME = TN-C-S.
Quite honestly, you need to ask all of these questions of your electrician. He is going to have to certify that HE/SHE Designed, Installed and Tested all of this.An electrician has agreed to this and will do all the final testing and certificates but as the house purchase hasn't gone fully through yet hasn't visited the property.
What are your thoughts with the TT earthing and the metal CU unit, there is the potential for the CU to become live and the DNO fuse not to blow due to the relativly high impedance of the TT earth
I have an MK metal CU unit that meets 17th edition 3rd amendment which I was hoping the electrician can install. From what I understand it should still meet 18th edition rules with TNS earthing. Its a split load x2 63A/30mA RCDs with 100A main switch, there will be x2 32A rings, x2 6A light radials and a 40A cooker outlet. Distribution of MCB's across upstairs and down stairs. I'm presuming the main DNO fuse is 60A. Appropriate labels for 6 monthly RCD testing and correct glanding for tails etc.
Do you think a 17th edition amendment 3 CU will meet 18th edition regs with respect to TT earthing?
I'm not a qualified electrician but am qualified in electrical and electronic engineering and plan to do a lot of the first fix work for my daughter to keep costs down, its her first property and money is tight. An electrician has agreed to this and will do all the final testing and certificates but as the house purchase hasn't gone fully through yet hasn't visited the property.
Thanks for your thoughts
A single RCD in an enclosure is not, by definition, a consumer unit so may still be plastic.Is there any point installing a separate 100mA S type RCD on the feed to the CU as I presume this would also need to be in a metal enclosure and simply moves the problem to that box?
Do you mean the Main Switch? If so, no and why would there be?Will there be a requirement to replace the main MCB on the CU to a 100mA 80A RCD?
We know that the (very rare) occurrence of a broken/'lost' neutral in a TN-C-S LV supply network can result in certain hazards, and that is equally true whether the supply is underground or overhead.Overhead supplies carry the risk of a conductor snapping in strong winds ( or if a vehicle impacts a pole ) If the Neutral snaps but the Live doesn't then a then PME ( TN-C-S ) "Earth" would not be at Ground potential. Quite hazardous. Hence the reaon why in the past PME "earths" were uncommon when the local supply network was overhead cables
However, I'm not so sure that that (very rare) occurrence is necessarily more common with overhead supplies than with underground ones