16amp blue socket wired off a socket spur
When I did my 16th we discussed radials for multiple BS4343 16A sockets, I think we established they could be protected with 20A MCB, however I don't find it in a very quick look in the book.
Can anyone else shed light on this please?
I have the same recollection.
I think it was something like "several BS4343 sockets could be supplied from a radial circuit not exceeding 20A". I'm trying to find the reg number..............
When I did my 16th we discussed radials for multiple BS4343 16A sockets, I think we established they could be protected with 20A MCB, however I don't find it in a very quick look in the book. Can anyone else shed light on this please?
The regs may say that (I can't remember, and don't have them to hand), but ....
If one sticks with the belief that the purpose of a sockets circuit's OPD is to protect the fixed wiring of the circuit (and not to protect {or 'limit' current to} anything downstream of the sockets), then I don't see what there should be any restriction regarding the OPD. In other words, provided only that the circuit's cable was of a CSA which was adequately protected by the MCB, I don't see why you could not have multiple 16A sockets on a 32A, 40A (or whatever) radial.
By analogy, as far as I am aware there are no corresponding restrictions as regards hard-wired (and 'unfused') loads - for example, I think that, theoretically, say, three 3kW immersions on a single 6mm² radial protected by a 40A MCB would be compliant, wouldn't it? If so, would three 16A sockets be materially different?
BS4343 plugs/sockets are unfused.
If your scenario were so, nothing would prevent the taking of all 40A through a single 16A plug ..............
You are not supposed to connect loads greater than 16A to 16A sockets - that is the point of them.
However, surely the name '16A socket', like 13A double socket, is just that - a name - the pins are definitely larger than 1mm² conductors so could handle current considerably greater than 16A.
I get what you're saying but it doesn't quite work like that does it? Thinking about the number of 13A plugs and sockets I've replaced [and not only the cheap makes] which are also considerably more than 1mm² where they struggle to run at 13A on a regular basis, demonstrates that to me on a regular basis.
I confess I'd be far more confident running 16A plugs/sockets [and for that matter any BS546] at a considerable overcurrent than our stupid 13A rubbish but after all said and done a rating is a rating and should not be exceeded.
The main current limit is surely down to the weakest link like contact area/resistance and possibly even the ability of making a good termination with the wiring.
Nothing at all wrong with 3x 3KW loads [or a submain to a CU] on a 40A MCB/6mm² cable.
However a 16A socket protected solely by a 40A OCD? NO. NO. NO! Far too many splitters out there.
BS4343 plugs/sockets are unfused. ... If your scenario were so, nothing would prevent the taking of all 40A through a single 16A plug ..............
Indeed not - but "So what?". As I said, if one believes that the (40A or whatever) OPD is there only to protect teh fixed wiring (and NOT to act as a 'current limiter'), the fact that the plug/socket was unfused would be irrelevant.
Indeed, even if you did think that 'current limitation' was one of the purposes of the OPD, a B20 would allow about 29A to flow for an hour, or appreciably more than that for shorter periods - hence not all that much use for 'limiting' current to 16A!
Do you believe that it is not permissible to have one (or morew) 15A BS546 socket(s) on a circuit with an OPD ofd >15A/.16A?
On Site Guide 18th edition, page 190.
Indeed. However, I wonder whether the fact that (as so often!) the OSG does not (cannot?) cite a regulation in BS7671 which actually says that may, perhaps, "say it all"?
Dad's garage had a C16 for the welder on the RFC - mounted on a metal box with a C16 MCB in it. Not regs compliant, but if you apply logic and electrical knowledge then you'd have to agree that it was perfectly safe (it was a short RFC, and the C16 socket would be not far of the middle of it).