Noticed this too.Has anyone with Wiser TRV’s noticed the reported temperature is about 2c higher than the actual room temperature since firmware ea64 was rolled out.
I dont know how well my boiler modulates, its a Worcester Bosch Greenstar 24i system boiler. I cant find any info in the installation or user manuals. I dont want to compromise boiler efficiency which needs low return temps but if only 25% of the radiators are "on" that must have an impact.Lot depends on how efficiently (if at all) your boiler modulates and how low it will go. Zoning is a good way to control your heat consumption but if you go too mad with it you can end up compromising comfort (for instance, if you have a downstairs room you don't use much so decide not to heat it the bedroom above may be slow to warm up).
I've gone the wireless TRVs everywhere- they work really well with the thermal store heated by woodburner- no worries about modulation ratios and cycling.
Minimum input on the 24i is 7.3 kw (page 6 of the install manual) so if you are only heating 1 or 2 rads the thing will cycle.I dont know how well my boiler modulates, its a Worcester Bosch Greenstar 24i system boiler. I cant find any info in the installation or user manuals. I dont want to compromise boiler efficiency which needs low return temps but if only 25% of the radiators are "on" that must have an impact.
Its a good point but surely Drayton, Honeywell, Hive, Nest, etc wouldn't agree as nearly all modern programmable thermostats now use TPI.I would argue against using TPI on a system which used to have an ON-OFF thermostat. TPI (time proportioned integral) will reduce the proportion of time that the heating is demanded as the measured room temp (mv) approaches the setpoint (sp), so for a 15 minute time period (4 cycles per hour) and with a calculated load of 33% (needed to keep the mv aligned with the sp) the output relay will be ON for 5 minutes, OFF for 10 minutes. The result will be 2-port or 3 port valves dancing around, up and down like a bride's nightie.
IMO TPI is useful only where Opentherm is in use, the calculated load being used to modulate the boiler's flow temperature. The Wiser hard-wired hubs have OT, I think.
That doesn't make them right though. My Honeywell Evohome is highly irritating in a standard S-plan configuration, for the reasons given above, but a joy when OT is used.Its a good point but surely Drayton, Honeywell, Hive, Nest, etc wouldn't agree as nearly all modern programmable thermostats now use TPI.
On my Wiser hub I can set the cycles per hour to 6 if I select gas or 3 if I select oil so there is some configuration there. My WB Greenstar condensing boiler doesn't appear to mind the 6 CPH setting.I'm glad I can turn TPI off on my thermostat. I don't think it can be good for my very old, cast iron boiler, to just come on for two or three minutes at a time, and not really get hot. And there must still be millions of boilers like mine. In my (limited) experience, TPI will provide extremely good temperature control, if left to do its thing, so maybe that's why the manufacturers promote it. But it comes at the cost of lots of cycling of the boiler and the motorised valves. I don't actually think most people need the room temperature controlling to the 0.25 degree level. I can see if TPI were set to say two cycles per hour, that would work OK, but the minimum on mine is six cycles per hour.
True but I would hope that the manufacturers technical staff that design these thermostats would have a pretty decent level of expertise.That doesn't make them right though. My Honeywell Evohome is highly irritating in a standard S-plan configuration, for the reasons given above, but a joy when OT is used.
I've seen that video, but I see it as more food for thought than a blanket rule.I was watching a video by Heat Geek who, if I understood correctly, basically said do not zone in my situation as the savings made by not heating all radiators will be lost due to less efficiency by the boiler.
In your first example I have a similar situation. I have 2 lounges joined by double doors which are open during the day but closed after about 19:00. The rooms have 3 radiators in total with the main lounge having 2 rads controlled by Wiser TRV's and a Wiser room stat.I've seen that video, but I see it as more food for thought than a blanket rule.
Example:
If you have a set of interconnected rooms that you want at basically the same temp, you might consider setting them up in Wiser as a single room. Wiser will average the temps, but any call for heat will be answered with max rad surface area.
Heat Geek's argument would say this is the way to go. I would say it's the way to go if one room has an undersized rad, because it'll avoid kicking on the boiler just to service that one room (particularly in Comfort mode - I have this issue and this was my solution). But if the rooms have similar heating and insulation, why not give control to Wiser and let it do the fine adjustments to keep the temps stable?
Another example:
I want my study hotter (+2 at least). Heat Geek's argument would tend to suggest that I should have that matched to the whole house, but I just don't need it that warm everywhere.
I compromised with a set point graph that initially heats it in concert with the rest of the house so that the boiler is mostly using all rads, and then steps it up over the course of the morning. This gives it a chance to get some heat from the Sun and my PC/monitor, and the boiler can just feed in small bursts (with Opentherm) to keep the rad warm without overshooting.
Re the TRVs, I would personally just stick Wiser TRVs on everything. Even with the not-stellar accuracy of the measurement, I don't really see the point of buying something like Wiser and then not using the smart TRVs - it looks like it's designed to operate as a system. You might as well buy a cheap wall thermostat and some manual or wax TRVs if you just want one zone all at the same temp.