https://www.diynot.com/diy/threads/...s-is-this-good-pic.483672/page-9#post-3927461 #124The question here is has anyone yet come across a melted leg(s) of a ring due to imbalance?
Draw a picture thenmaybe what im saying is being misunderstood
They can certainly pass more than 13A per socketa fixed double gang socket can only take 13amp ? across both its points not 13amp on each point
Yes, we know that story of yours
Draw a picture then
Sounds like you're talking about this:
No the fcu would need to be before the first socket, if you wanted more than one.Yeah this one is kind of correct but its not coming out the back of a socket on the ring its coming from a break/juction box in the ring
So you cant break into a ring run a single lenght of 2.5mm to a new double socket the spur off that socket with fcu
A double socket is a break in a ring/there is no difference between a JB and a socketSo you cant break into a ring run a single lenght of 2.5mm to a new double socket the spur off that socket with fcu
I feel the need to start from the beginning here.Hi guys can anyone answer a question im intrigued by
The "normative" part of the regs does not explicitly say how many sockets are allowed on a spur, but there is guidance in an appendix that specifies one single or double socket. There is an implied assumption here, that it is "unlikely" that both sides of a double socket will have large loads presented at the same time. The test requirements for sockets in BS1363 have a similar assumption.you can spur off any part of the ring with only 1x double socket
To comply with the guidance, the fused connection unit must be located such that it protects *all* the sockets on the spur.however i believe its permitted that you can add a 13amp spur unit from the spurred socket and then run as many sockets as you want from that being protected by the 13amp unit
No it's not typical of a domestic property... ButYes, we know that story of yours
For a start, it's hardly a typical domestic situation, with a welder drawing 40 A (with peaks of 200 A) from a socket 2m from the end of a ring protected by a D32!
However, as I'm sure I've said before,I still don't see why 2.5mm² cable should come to any harm (let alone 'melt') in that situation, since we know from a combination of the regs and the characteristics of MCBs that a cable is deemed to be able to carry 1.45 times its 'rated current' continuously for an hour without coming to harm. Method C 2.5mm² cable should therefore be OK with up to about 39A continuously for an hour.
Yes, work out how much current could possibly be in the cable and if it is more than the cables rating then it is not allowed - except of course the guidance that only one single socket may be on an unfused spur - we wouldn't want everything to be totally clear.ok i understand now so your not suppose to add a fcu to a socket that has already been just ran off on a single 2.5mm cable and is not part of the ring
the way to do it would be change the socket that has been ran off the single length of 2.5mm to a fcu then add further sockets after that
Well yes but there is no point having two FCUs - and are they not all double pole nowadays?just another question i have single socket in my loft that is running off a fcu that is in my living room which come off from a socket
can i ask would i be able to change the socket in the loft to a double pole fcu with a 3a fuse to be able to run my extractor off
Surely a socket ON the ring.so it would be socket off the ring going
Change the first FCU to 3Ato a 13amp fcu on 2.5mm which then would run to a second double pole fcu with a 3amp fuse which would then run to a pull cords and then to my extractor on 1mm twin and earth
Correct.ok i understand now so your not suppose to add a fcu to a socket that has already been just ran off on a single 2.5mm cable and is not part of the ring
Correct again.the way to do it would be change the socket that has been ran off the single length of 2.5mm to a fcu then add further sockets after that
Ifthe socket in the loft is fed from an FCU, you don't need a second one. Since that socket is already downstream of an FCU, you can connect any number of additional sockets (or anything else) to that socket.just another question i have single socket in my loft that is running off a fcu that is in my living room which come off from a socket ... can i ask would i be able to change the socket in the loft to a double pole fcu with a 3a fuse to be able to run my extractor off
I believe you currently have thisjust another question i have single socket in my loft that is running off a fcu that is in my living room which come off from a socket
so it would be socket off the ring going to a 13amp fcu on 2.5mm which then would run to a second double pole fcu with a 3amp fuse which would then run to a pull cords and then to my extractor on 1mm twin and earth
Quite so ....No it's not typical of a domestic property...
That is a pretty crazy (and non-compliant) design. If all of those loads were actually AT 2 metres from origin of the ring, then the short leg of Method C 2.5mm² cable could never become 'overloaded' (provided the total load on the circuit did not exceed the design current of 32A) if the total length of the ring were at least about 11 metres.But ... What is typical it a ring covering the whole house, yes even now there are many houses like this - a neighbours CU is in the back of a kitchen base unit, in the first part of the ring is the multiswitch serving: dishwasher, washing machine, tumble drier, fridge/freezer etc, immediately followed by three double sockets for: kettle, toaster, microwave and airfryer etc all within the first 2 metres ....
That obviously means the the circuit was loaded far beyond its design current.... their electrician placed data logger clamps on both legs and there were frequent instances of 50A on one leg which I assume was the short.