Hey @Madrab Do you know if the Worcester Greenstar Life 36kw System boiler has an Auto bypass valve or not? Couldn't see mention of it in the user manual.It'll be in the book of words - Bypass rads are no longer an acceptable method for bypassing boilers and I don't believe the 8000 has an internal bypass.
If there is a possibility of the pump pushing against a closed head - all the valves in the system are shut down - then an auto bypass would be required to ensure min flow through the HEX on overrun.
No - the boiler modulates down to maintain the output set tempsThe boiler then modulates down to 50% and I presume that’s why it’s taking ages to get the rads hot.
Are they vertical column rads or are they vertical tubular designer rads, the former isn't described as a designer rad, the later is and they are quite different, if you see what I mean.4 triple column designer types.
A T50 rad, assuming a room temp of 20C with a flow temp of 75C will require a return temp of 65C to give its rated output, it will output ~ 6% more if the return temp is 70C as it is now a T52.5 rad, obviously the lower the return temp, the lower the rad output, just feel the boiler return pipe, you will get some idea of it's return temp by doing so.Target temp is 75c.
It’s 36kw, and when I add up the kw of the rads at T50, the power requirement for them is around 28kw or so.
As far as I can see, it doesn’t have a read out for the return temp. But I guess I could tape one of my fish tank temperature monitors on it and see?
I have been wondering if the boiler heating up so fast is because the pump is either too fast or too slow…I guess either could cause that to happen. But if the return temp is returning very hot would that suggest the pump speed is too high? And if the return temp is low, would suggest the pump speed is too slow?
75deg these days is a bit too hot TBH and If the boiler is overshooting its target temp, then there may be a flow/circulation issue. TBH though it could also be that the system hasn't been balanced properly and that's adding to the slow flow/circulation. What size of pipework is being used? 22mm > 15mm or smaller and is it all the same? Running the boiler in sweep mode just hi fires the boiler for up to 15min or until it overheats
As suggested an ABV wouldn't have anything to do with that.