Checking Earth is actually earthed!
4 Feb 2006
What's the easiest way to check that my earth is actually earthed and that there are no breaks. Do I just apply a voltmeter across the live and earth wires and if reading is approx 240v thats ok?
The only proper way to test it is to take a reading with an earth fault loop impedance tester.
A volt meter would give a crude idea, but you can get a reading of 230V between live and a wall or floor. I wouldn't rely on them to clear a fault.
An EFLI test will verify if there's a path to earth, not necessarily by the cpc, for example, parallel earth paths via water or gas bonds though supplementary bonding and cpc's connected together in 2 gang switches for upstairs and downstairs lighting.
The only way to check you have a continuous cpc would be to perform a R1+R2 test correctly.
Doing an R1+R2 would prove continuity, but wouldn't prove it is actually earthed, unless you tested Ze in isolation.
Not entirely clear what the OP is trying to acheive, but I reckon R1+R2 and Zs for each circuit, and Ze should cover it.
Well guys, you've complete lost me there :lol:
Reason for the question is that I live in the house that jack built and it seems every time I do a job I find something more to worry me. I've just found out that I don't appear to have continuity in the ring circuit (i.e. only one side live). That's wrong innit? The house is about 30yo.
Other things I have come across are diagonally laid wiring in the walls, copper wire for a lighting fuse and random earth wires burried in the plaster (no idea where they lead to!).
The reason for the earth check is purely for my piece of mind rather than a thorough investigation but if your saying that's what I need then I'll get someone in to check it over.
Thanks again.
Darren, it would be an idea to get a competent electrician to carry out a PIR (Periodic Inspection Report). This will (or should) highlight the current state of your installation and any repairs that are needed.
That sounds like a good idea Gary. Any idea how much a PIR should cost roughly on a 3 bed detached property?
That could depend on a few things. A company may just put a day against the testing and creating the report meaning anywhere from £120 to £200 and upwards
Others may charge per circuit.
Is your earth connected to the right hand side of the mains service fuse block? (that big black thing next to the meter, containing a large fuse between 60-100 amps for a house).
Or is it connected to the outer covering of the mains service cable, through a thin wire lead?